Although you should always leave the CPC connected to the MET when doing an IR test
According to the latest edition of GN3, the requirement to have the CPC connected to the means of earthing while doing IR testing was introduced in the 17th edn, 2008. Para 612.3.1 of 7671:2008 amd1 refers.
Of course, if you're just fault finding, as opposed to certifying, you can do what you like within reason.