I
imago
If we set aside Part 'P' and testing with an MFT for a minute, you still can, and should be able to carry out tests. People were testinmg installations long before the dual 'cure-alls' of Part 'P' and MFTs came along.
So, you shouldn't assume or guess that earth leakage from the new appliance is responsible. It may well be a red herring, and possibly cost you a great deal of time looking for a fault which doesn't exist.
Back to basics, disconnect everything on that circuit. Does the RCD still trip? If it does, investigate the wiring. If not, reconnect the appliances/equipment one at a time and operate them. Does it trip out? If yes then you've narrowed the fault down. If no then get them all operating together one at a time until it does.
95% of electrical faults can be found using very basic principles and a systematic approach. An MFT will speed up the process, but basic test kit will quite often get you there. The issue being that everyone wants to sort out a fault in an instant and rushes the job. There also seems to be a worrying lack of understanding when it comes to basic principles generally as the younger/newer qualified sparks seem to be taught stuff parrot fashion when it comes to calculations and testing, rather than building up to that from the basics.