Sounds like a guess. If its not in BS7671 and you can tget information from the manufacturer then you will be guessing.
Although 2.5mm is rated around 27A (clipped direct and depending on its run), the ring will not necessarily put equal load on each cable and hence the 32A device. In your case the cables may well be the same length and therefore in theory should split the load equally. But this does not take into account resistance at the terminations. again this is an unknown. in the event that one side comes free, a 32A MCB will be just enough to protect the cable. In your sitaution it will not be and you will have a fire.
You cant back yourself up in a court case with guesswork. If you go by BS7671 then you will not have unknowns and you will not be guessing. No one will be able to argue.
Although 2.5mm is rated around 27A (clipped direct and depending on its run), the ring will not necessarily put equal load on each cable and hence the 32A device. In your case the cables may well be the same length and therefore in theory should split the load equally. But this does not take into account resistance at the terminations. again this is an unknown. in the event that one side comes free, a 32A MCB will be just enough to protect the cable. In your sitaution it will not be and you will have a fire.
You cant back yourself up in a court case with guesswork. If you go by BS7671 then you will not have unknowns and you will not be guessing. No one will be able to argue.