Despite everything we get told about supply voltage it is not 400/230V.
Most UK LV distribution transformers are:
11/.433/.250KV.
Tapings (if fitted) -5% / -2.5% / 0% / +2.5% / + 5% (set at 0%).
Reactance 0.45% up to 1000KVA, 0.5% above.
Voltage regulation is normally at the 33/11KV transformers with OLTC’s.
I tried lowering the LV voltage to 400V on 4 X 20MVA transformers as an experiment. Got nothing but complaints!
No pleasing some people!