How are you going to damage a cable with back fill if done properly?
Do the job properly, use the armour, gland and earth the end correctly. Can’t be any simpler really.

If you’re worried you can carry out a sheath test. But if it fails you’re shafted anyway.

I better off not go back and some tests on my garden jobs!
 
What's the norm on a 3 phase Submain in regards to swa and earthing, I'm looking at 25mm swa but not keen on using the armour as earth, (it works out ok size wise) I normally use an extra core for earth on single phase but 5 core swa seems a bit thin on the ground anyone have fors and againsts for usin the armour?

Single phase SWA...........3 core dedicated earth.
3phase/N. SWA.........5 core with dedicated earth( neutral distributed or not).
That's me every time.....bwtfdik:)
Solid 6mm brass bolt and nut earth throughout.

Nothing wrong with either method mate...........properly installed lol

- - - Updated - - -
 