M
mamba
9 LED outside garden lights protected by RCD. Originally the client asked me to investigate outside lights as when he switched them on RCD tripped immediately . On investigation found previous Halogen fitting past sell by date most full of water and corroded. Client agreed to have all replaced with IP65 LED's. Have now replaced all fittings IR tested all cables prior to fitting new LED's all good. Also RCD test done + Ramp test Ramp 27Ma and trip times all good. However when Turn On supply RCD does not trip immediately buy holds and then trips anything between 50 seconds to over 6 min. Other than dismantling each light to ID possible rouge light any suggestions?