Davem

Evening gents bit of advice required please I have recently finished a partial rewire (upstairs sockets upstairs lights and smokes). All is fine apart from when I turned under unit lights on in kitchen it tripped both rcds. There is 1 2 gang switch in kitchen 1 for main kitchen light and 1 for under unit I have taken link out from main light switch the under unit light switch and this rectified the problem no tripping but when I put link back in both tripped again and ideas guys cheers by the way pretty new to the game so be nice
 
You need to carry out an IR test on the suspect circuit, more than likely a NE fault.
 
Big mistake mate with the "new to the game" and "be nice bit"..tripped both RCDs?? christ why does none of this exciting stuff happen to me?
 
Hey little bit of advise, type your post up in word, then go away for 10 mins or so, then come back and read it, edit it then post it.
 
Back there tomorrow guys working Sundays love it so will do as advised I have tested all new installation and all is fine gotta test old bit tomorrow looking forward to it a will get back to you with results cheers guys
 
It's more important to test the existing installation prior to installing a new board. It will save you being in the situation you are in now.
 
bet it's a shared neutral between 2 lighting circuits or a N in wrong bar in CU.
 
bet it requires a bit of simple logical thinking and some know how and possibly a dash of electrician
 
No borrowed neutral all lighting is segregated to individual circuits Everything works fine other than under unit lights
 
Where are the under unit lights switched from? I had a similar problem once . They picked the live from the kitchen switch and a neutral from a kitchen socket.
 