M
MDJ
The Rcd is faulty and there is a dodgy ring on the hob, test the rcd as per usual, at times half, one and five on 0 and 180 degrees, that will sort that bit out, then you can look at whats going on with the oven.
Not a dead short at 92 OhmsIf the cooker is on and it's leaking >30mA why has it not tripped then?
2,500,000 / 1000 gives milliamps Leave I in Amps, not Milliamps
A = 2.50A
IR = 230 / 2.50
IR = 92 Ohms
if I'm correct in my calculation you have a almost a dead short somewhere?
Dead short? We got slaughtered for saying that on the 2391.
Its a joint of negligible impedance that exists, acording to the lecturer!
Boydy
It has got me thinking and cannot work on it further until landlord gives permission. Thought it might give a few of you a puzzle to think about on your sunny Sunday afternoon. I am puzzled as to why the RCD has not tripped because outwardly it looks like a Neutral Earth fault, but I have not checked yet to find out more specifically where the the problem is. The lighting and smokes are not on the RCD. Also as someone, has mentioned here already, the occasional RCD trip could be unrelated to this high residual current. Hopefully I'll get the job and will be able to satisfy my curiosity.
The 'occasional trip' and the 2.5A leakage current don't really go well together. 'Won't reset' would be better.
Measuring the leakage down the CPC or main earth doesn't show you what's being lost down parallel paths so it's not the most accurate way of testing..
Is it a single RCD or dual RCD board?
not a `dead short` anyway...as its earth fault...Not a dead short at 92 Ohms
hot?...or just measured cold?Ah yes, the current in Earthing Conductor is just part of the story. In this case it is in a block of flats so the services main bonding paths in the flat could be nicely carrying a proportion of any earth leakage current. The RCD "occasional" trip could be something else and may not even happen again. The tenant's brand new very basic cooker IR is OK, the install of this was the reason for being there in the first place.
do you think this would do the trick?It may be accumulated unless everything else is disconnected but still, I would expect to have to use an elastic band or a lock out device to hold the RCD on.