EddieB

-
Arms
Guys advice please on a report that has come my way to undertake remedial action, there is one item I'm not sure on how to approach it states
" No RCD protection on cables buried less than 50mm from surface of wall" The ring circuits have RCD coverage, so it's the Lighting that this statement concerns. This is a let property with shared occupancy. It's been given a C3 classification.
 
IMHO stating "requires improvement" means that the only logical thing to do is update the CU which isn't fair on the millions of homeowners with 16th ed or earlier homes!
 
tell them a new cu would improve the situation and the price of doing the work. explain it's to an earlier version of the regs and still reasonably safe. then see if they want the work done. i find about 60% agree to a new cu if you explain the benefits well enough.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

EddieB

Arms
-
Joined

Thread Information

Title
Domestic Condition report
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
EddieB,
Last reply from
Risteard,
Replies
27
Views
4,433

Advert

Back
Top