  1. HappyHippyDad

    Fault find or rewire?

    Just spent 4 hours tracing out a lighting circuit to try and find a fault. I came across a switch that was switching the neutral. This threw me as I was getting 230V on the S/L (to earth) at the light when I switched the light off!!! I then realised the Neutral was being switched, which I...
  2. M

    Earth to Neutral 2 ohm with Multimeter cable disconnected from switch board.

    Earth to Neutral 2 ohm with Multimeter on alighting cct. The cable disconnected from the switchboard. I am new here and appreciate everyone looking at this post. I come from an Industrial Electrical background and would like advice on fault finding. My house has 1 lighting RCD. There seems to be...
  3. S

    Kitchen LED Strip Light Fault

    Hello, We moved into our house 2 years ago and until recently the kitchen lights worked fine. The LED strip lights are on a dimmer switch, when pressed (full power selected) the LEDs come on briefly and then go off. On investigation the LED strips are driven by an Aurora driver (this model...
  4. S

    Hi, question on Fault finding L-E

    Hi all, what appliances could show really low ir results between L-E? And give a Kohm reading instead of ohms reading L-E? Thanks
  5. S

    Zs and Ze - both called 'Earth Fault Loop Impedence'?

    Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
  6. J

    Mains electric shock from plastic light switch - no fault found by electrician - what next?

    Hi all! This is my first post and I have registered to ask for some help with troubleshooting an electric shock I got from a plastic light switch outside a bathroom today. I turned the switch off with my left hand and got what felt like a mains electric shock through the switch into my left...
  7. L

    Freezer fault has me stumped. Hotpoint FFUL2023

    I experienced the common issue of the condenser frosting up so the air can't circulate around the freezer or up into the fridge so it all gets warm. I defosted the condenser as it was solid ice and it all got cold and was fine for a week or so but has frosted up again. The defrost heater was...
  8. captaincaveman

    Best way to locate a fault in garden 12v lighting

    Hi Guys n Gals, I'm a little stumped on a job and was wondering if anyone could advise? I've got 3 drivers going to 3 sections of garden lights. Two of the three sections are not working (about 10 lights). I presume it's two sections due to the number of lights and I can't find a third section...
  9. W

    GARO PME fault device, resetting

    Hello, Just had a client call saying EVCP was not working. It is supplied via a 'G6EV40PME' from what he was saying it looks like this cut out the supply, I cant remember if this device is self resetting when the voltage monitored is within range or if you have to reset the device by tripping...
  10. The apprentice

    Fault on ring circuit (weird)

    Hi there was called to a job with fault finding on a ring 120v on one socket 190 on the other the guy had been doing some work in the kitchen by removing a socket and joint it straight through now it leaves the board as a radial so I had taken one socket of getting voltage on the earth and when...
  11. D

    Prospective fault current testing

    hi, new to this forum and still training. During testing for prospective fault current at the point I get a bad reading, what ever that may be????, what possible situations would be causing and why? still trying to get my head round it... thanks Adam
  12. J

    Phase to Earth fault on a 3 phase motor supply

    I had the 20 amp 3 phase breaker off and was testing for voltage at the motor terminal box. I had nothing between phases but had 230 volts from each phase to earth. Why might this be.
  13. A

    Arc Fault Protection

    Hi Everyone, question. Have furnace in basement (nothing else in basement besides electrical panels - not finished basement). Inspector is saying furnace is required to be on arc fault breaker. Per NEC 210.12, I completely disagree. Any input would be most appreciated. Thanks
  14. W

    Intermittent Tripping Rcd fault

    Feel like I’m posting on here every week for advice :) is a reading of 0.18 megaohms between neutral and earth enough to trip and RCD. Sent to an intermittent Rcd tripping, everything else seems clear bar this one cable. As always nothing tripping while I was there. Ramp tested the RCD and 15ma...
  15. K

    Price for fault finding? ££

    What do people charge for fault finding for a domestic customer?
  16. A

    Can a BS 61008-1 RCCB be used for fault current protection

    I am aware that a BS 61008 can't be used for overload protection but is there a reason that it can't be used for fault current protection.
  17. W

    Fault on lighting circuit

    All CPCs on upstairs and downstairs lights were live due to the cpc of upstairs being disconnected from earth bar. I was getting 230v between cpc and neutral at the light, the 2 circuits are separate and the rcd never tripped, anyone had this before or know why this would happen
  18. A

    Anyone ever had a L to N fault in a brand new socket

    I have just spent about 6 hours in a freezing cold building tracing a continuity fault between L and CPC in a ring final circuit in an outbuilding. Not yet commissioned. This has 8 pairs of Hager SS flush double sockets in it (ie 16 sockets) above a quartz counter, and 4 double sockets beneath...
  19. R

    UK Fault with ring main

    I was testing a consumer unit before upgrading to current standards. (Old re wireable fuses) when testing one of the ring mains continuity i found 38v on the cpc with that circuit disconnected. After carrying out end to end tests on Line and neutral which came back fine. I found the voltage...
  20. A

    Failed my AM2 fault finding 3 times….please help!?!?

    Failed AM2 Fault Finding 3 times!!! hope somebody can help me, I’ve spoken with the examiner, he said my fault finding itself is fine it’s just my writing/explanation. Can someone give me some examples of what to write so I can pass it this time!? Thanks