tails

  1. G

    Which tails for Garo / Matt-e

    Hi all, Hope you are all well and all is good. Was just wondering which tails you guys use to go from a Henley block to a Garo / Matt-e EV unit. I'm fed up of fighting with them, are there any super flexible ones and what size do you tend to use? Also which cable glands do you find the...
  2. T

    Tri rated meter tails or flexible meter tails

    Hi everyone, Bought some Flexi meter tailes from a supplier today , Am I going crazy or that I marked up incorrect . The Flexi tiles I’m used to has 19 strands of copper or similar, opposed to the normal six or seven. The ones I’ve got today, Looked like finally stranded wire, at least 200...
  3. T

    Running meter tails outside in trunking

    Hi everyone, hope you’re all doing well. Got a job starting next week for a rewire of a studio flat, currently they have 10 mm T&E as metre tails , So definitely got to be an upgrade. The existing meter box is situated outside ( under cover ) the bathroom wall , On the right hand side of the...
  4. A

    Meter tails over 3m

    Hi Guys Just some advice required. I understand meter tails ideally at 3m from meter but is it possible to have meter tails 10-15m from the meter? Came across a job where there's no real option but to have the consumer unit 10-15m from meter cut out. If it is possible is additional...
  5. Kuba

    Meter tails size

    What is the size of these meter tails? Are L&N going to the meter 32mm or 25mm and coming out are 25mm or 16mm? Permitiers are roughly 40mm of larger one and 35mm of smaller one. Thanks for your help ?
  6. captaincaveman

    25mm SWA for tails chased in wall

    Hiya. I suspect I already know the answer to this but I would welcome any opinion from anyone who's tried it... Moving a domestic consumer unit 2M up a wall. Ideally I don't want to use trunking. Debating whether I could get away with 25mm SWA chased into the wall but I don't recall using 25mm...
  7. newfutile

    10mm Tails size

    During a recent EICR I have found 10 mm supply to the flat This is fed from a Locked ryefield DB though a meter then a double pole 100 amp Isolator , the outlet from the isolator is the 10mm 3 core possibly hightuff cable This is over sleeved into the isolator. My question is would the...
  8. A

    Meter tails >3 metres in length

    Hi Has anybody ever found where this "rule has come from"? In the NAPIT codebreakers book it quotes "ESQCR regs" but it is not actually written in there. If it is a DNO rule then it comes under their regs (ESQCR), but as I said, it is not in there....
  9. E

    RCD protection on these tails and why 2 isolators?

    Hi all I have a few questions about that video. 1. I don't understand why there are two isolators on the tails between the meter and the CU. One is fused and one isn't, so what's the point in the one that isn't? 2. Why would this 'require RCD protection' like the guy in the video says? I...
  10. BigSpark

    1.5mm meter tails

    Evening All, I attended a job today to disconnect an Alarm System at a ground floor flat. On taking the consumer unit front off, discovered the incoming neutral tail to be 11 x 1.5mm single core cables which needless to say aren't all tight and secure in terminals. The incoming line looks to be...
  11. D

    Fused main switch - tails over 3m

    A quick question regarding tails and the 3m length. I need to move a consumer unit, however it will be around 5m from the DNO cutout. Is it acceptable to install a REC2 isolator at the meter cabinet, 3m tail length to an accessible position and then a fused main switch, followed by around 2m of...
  12. kropaske

    Cloth covered tails advice

    Been asked to price CU change but i am concern about tails between cut out and meter. I'ts top floor maisonette and main cut out is in the cupboard downstairs by the front door. From there cloth covered tails run in metal conduit(which is used as main earth) approx 10 meters to the cupboard in...
  13. E

    Meter tails in ceiling ?

    Hi all, I am moving a CU from next to the meter to about 1.5 meters away on an adjacent wall. Am I OK to run the meter tails through the ceiling void between the joists (plasterboard ceiling) to the new CU position or is a case of installing an isolator and 25mm swa? Many thanks
  14. Marcus Vaughan

    Coding question - Twin and Earth Tails

    As above really. First time I have seen this but its basically 16mm twin and earth connected straight into the outgoing side of the meter, and into the consumer unit. Quality. Couldn't quite get a picture of the external MET but can confirm an additional cable has been added to bring the size of...
  15. D

    25mm tails why..?

    Have you ever come across a melted 16mm tail ? Me , no never ... why are tails expected to be 25mm , seems utter overkill imo thoughts
  16. Weezy

    UK RCD protection to Meter Tails?

    About 20Meters of 25mm meter tails are routed though the floor boards feeding a sub main. To protect the tails under the floor i was going to fit a Mini Metal Unit with RCD protection Fused at 50A at the mains position, Just wanted to check to ensure it’s a 30ma ‘S Type’ RCD i need? As the c.u...
  17. A

    Upgrade tails on CU replacement?

    Hi. I have my NAPIT first assessment soon and I replaced a CU in a house which has 16mm2 consumer tails in place. I did not upgrade the tails to 25mm2, so my question is should I have upgraded them or am I allowed to leave the existing tails in place? I do not know the rating of the DNO cut-out...
  18. D

    Meter Tails, recessed box

    Hi all, Waiting for a bashing here, but it's something I haven't had to do until now so looking for advice on the best way to approach this. I've been asked to replace a consumer unit for a customer but the existing meter box is recessed in the exterior wall - not uncommon I know, but not...
  19. S

    Protection of Meter Tails and Length

    Good Afternoon All, I have just completed a Periodic test on a house and have a question about the meter tails. The house is 14 years old so has 25mm meter tails. The CU is in the garage and the meter box is around 7m away on an external wall as you'd expect. Looking at it, I imagine that the...
  20. W

    Mechanical protection for meter tails

    Does anyone know if there is a product for protecting mains tails in walls apart from conduit? In sure ive seen stainless steel capping or something similiar that can be earthed and is drill bit resistant?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock