Hi all I have a few questions about that video.

1. I don't understand why there are two isolators on the tails between the meter and the CU. One is fused and one isn't, so what's the point in the one that isn't?

2. Why would this 'require RCD protection' like the guy in the video says? I thought we normally went supply -> meter -> main switch -> rcd protected board.

3. If this does actually need RCD protection where would it go? Between the fused main switch and the CU?

Thanks for helping me out with my newcomer questions.
 

Hi all I have a few questions about that video.

1. I don't understand why there are two isolators on the tails between the meter and the CU. One is fused and one isn't, so what's the point in the one that isn't?

2. Why would this 'require RCD protection' like the guy in the video says? I thought we normally went supply -> meter -> main switch -> rcd protected board.

3. If this does actually need RCD protection where would it go? Between the fused main switch and the CU?

Thanks for helping me out with my newcomer questions.
The first isolator is fitted by the DNO the second one is to give the cable a fuse for fault protection if the board is over 3m away, the tails only need rcd protection if they're less than 50mm in the wall
 
Ah . Chris the plumber . Haven’t seen one of his vids in a while .

2 switches , presumably the Dno installed the first one and the builder fitted the second one to fuse down the the supply.

30 ma rcd protection is required if they are 50mm or less from the finished surface , this you simply can not ascertain from the video footage

Chris the plumber mentioned earthed metal containment which is another option but extremely rare in domestic work
 
On a side not , not really sure why he is moaning about the top of the isolater, yes strictly speaking the gap is greater than 1mm but it’s hardly an issue inside a locked meter cupboard.
there are millions of meters and isolater switches up and down the country just like it...
 
The first isolator is fitted by the DNO the second one is to give the cable a fuse for fault protection if the board is over 3m away, the tails only need rcd protection if they're less than 50mm in the wall
Ah right - howcomes the DNO, seeing as it's a newbuild so they knew where the CU was going to end up - didn't just put it straight into a mains fused isolator?

Just confuses me since (even though one is fused) we can isolate it from either one of those so the unfused one is literally pointless isn't it?

Or is it a case of 'we've put one in and done our job, you need to put in whatever you need after and that's your responsibility'?
 
Ah right - howcomes the DNO, seeing as it's a newbuild so they knew where the CU was going to end up - didn't just put it straight into a mains fused isolator?

Just confuses me since (even though one is fused) we can isolate it from either one of those so the unfused one is literally pointless isn't it?

Or is it a case of 'we've put one in and done our job, you need to put in whatever you need after and that's your responsibility'?
I’d imagine the DNO had no idea where the units would be mounted finally, nor cared, they’ve supplied and protected they cables ?
 
I’d imagine the DNO had no idea where the units would be mounted finally, nor cared, they’ve supplied and protected they cables ?
Ah ok so makes sense - they just said 'right our job is done' which meant the spark doing the job then had to put a fused breaker in?

I'm still a little confused as to why - aren't we 100a protected where the supply enters the building? This particular one goes through a meter then through an unfused isolator to then be put through another 100a (?) isolator?

What's the point in two lots of 100a fusing?
 
Ah right - howcomes the DNO, seeing as it's a newbuild so they knew where the CU was going to end up - didn't just put it straight into a mains fused isolator?

Just confuses me since (even though one is fused) we can isolate it from either one of those so the unfused one is literally pointless isn't it?

Or is it a case of 'we've put one in and done our job, you need to put in whatever you need after and that's your responsibility'?
The metering supplier because its a new build are not responsible for the final connections/testing etc, therefore an isolator is fitted as a demarcation point.
 
What's the point in two lots of 100a fusing?
The point is who owns the fuses. The DNO's cutout protects their network, service cable and meter, but is not to be relied on to protect the customer's equipment because it's not the customer's property and is not accessible to them. It is acceptable for it to protect up to 3m of tails as this represents a low risk. If the layout involves a longer run of cable that is part of the installation although before the CU, then the DNO can't take responsibility for the adequacy of their fuse as protection for the cable and the customer is required to provide their own.
 
The point is who owns the fuses. The DNO's cutout protects their network, service cable and meter, but is not to be relied on to protect the customer's equipment because it's not the customer's property and is not accessible to them. It is acceptable for it to protect up to 3m of tails as this represents a low risk. If the layout involves a longer run of cable that is part of the installation although before the CU, then the DNO can't take responsibility for the adequacy of their fuse as protection for the cable and the customer is required to provide their own.
I see, good explanation thanks.
 

Reply to RCD protection on these tails and why 2 isolators? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
832
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
443
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock