Firstly I'd say you shouldn't be using a 13a FCU as it's right on the limit with a 3kW Immersion heater - much better is a good quality 20 amp DP switch and it should be fed via a dedicated 2.5mm circuit from a 16a MCB or RCBO. As for the flex, 1.5mm minimum.
 
1.25mm is on the limit for 13A anyway, more so in a hot area so I would also go 1.5mm

Agree with the FCU, not needed for a dedicated circuit anyway, and an indication it might be off a RFC which is not good practice.
 
If it's on a 16A circuit, then the fuse in the FCU is not required, so the FCU should be replaced by a 20A DP switch. A 13A fuse will run hot feeding a 3kW immersion heater, and the plastic of the FCU will be damaged over time.
 
If it's on a 16A circuit, then the fuse in the FCU is not required, so the FCU should be replaced by a 20A DP switch. A 13A fuse will run hot feeding a 3kW immersion heater, and the plastic of the FCU will be damaged over time.
Cheers Brian I thought overload protection wasn’t required. Looks like these were initially installed like this.
 
So best option is to replace the flex to 1.5 and replace the FCU with One of these?
 

Attachments

  • CB5B7AA1-9322-414D-B3CE-65EFAC0BAF7E.png
    CB5B7AA1-9322-414D-B3CE-65EFAC0BAF7E.png
    374 KB · Views: 93
So is this an occasion where regulation 433.3.1 comes into play? I will make this 25 characters long to comply with these rules. Just about 25 😂
You were at 25 characters at the “e” of “regulation”
25 words would be longer.

I’m not sure what this limit achieves…. Apart from stopping someone spamming threads with one letter posts just to be annoying.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Maintenance Electrician

Thread Information

Title
1.25 flex of a 13 amp fused spur feeding a 3KW immersion heater
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
Jako13!,
Last reply from
littlespark,
Replies
12
Views
10,149

Advert

Back
Top