Currently reading:
10.5kw shower
Discuss 10.5kw shower in the UK Electrical Forum area at ElectriciansForums.net
Yesterday smelt a weird smell of burning/melted plastic in my bathroom after some looking about realised was the shower pull cord opened it to the the incoming live insulation completely melted an charred and the pull cord terminal melted shower was installed about 3/4 years ago but recent board change by council(council house), I've done a cable calc and l got a Ib of 45.65 A so next suitable breaker 50A and got a 10mm t&e, currently on 6mm 40A breaker. Would you reckon this was the reason it had melted or due to other reason?
Ps have isolated removed switch and stopped using shower
no, In < Iz. so that the MCB trips before the cable is overloaded. so if Izis 47A, then a MCB below 47A In is selected.
you get a little warmth at the terminations in the switch due to load current. this leads to expansion/contraction leading to a slightly loose connection after time. this then starts to arc, burn, and before you know it here comes fireman sam with his hose.
To be honest I doubt that a 6mm cable would have melted on a 45/50 amp supply unless the cable was sub standard and there have been cases of that.
More likely the switch had melted due to
a) Loose connection
b) Moisture getting into it and shorting
c) Cheap and nasty accessory ( same as cable could have been)
d) Old accessory that was rated 45amp and finally broke down
the 40A breaker will protect the 6mm from overload. start off by replacing the switch for a good quality one, crabtree round ones have good reports. then with the shower going full heat, clamp the L core in the DB and see what it's drawing. i'll be surprised if it's > 40A.
Busy on the Bond thread Tel lol ..................how you feeling mate, sort out the transport?
yep. picked up a nissan, same model on a 51 plate. £900. needs a mirror and a couple of other bits off the old one, which i.m keeping for a bit as a donor vehicle.
It did get damaged, so no need to upgrade cable or breaker? And I was guna replace it with cooker type switch in airing cupboard and don't have the equipment to test only a apprentice
If your an apprentice then surely your sparks would either lend you the meter or come round and assist you, in assist I mean watch how you perform
You can pull the cable into the airing cupboard, but then your dicing dangerously near the dreaded part P if your in England and Wales, and after all you said this is a council house so either let them sort it, or just change the pull switch like for like
what's wrong with fitting a wall mounted shower switch. they're far more reliable than the ones with a bit of string. just need a longer bit of 6mm from sw. to shower.
edit: switch will need to be outside the bathroom , of course.
Yeh my boss or the other sparks on the firm will probably Assist me just discovered it yesterday so haven't spoken to or seen then but will tomorrow, boss doesn't currently have a meter is replacing it soon due to having the van stolen with all tools, power tools, testers, materials stolen a couple weeks ago only just replaced the power tools. Just wanted to check that cable or breaker didnt need upgrading first before anything else
strip back the cable. fit new switch. then borrow a clamp meter from work and do what i suggested earlier.
Reply to 10.5kw shower in the UK Electrical Forum area at ElectriciansForums.net