If the cables to the new CU position are to be concealed in any walls, then it’s very likely they will need RCD protection.
If however they are just going to run up the surface of the wall into the ceiling and along to drop down into the new CU, RCD protection will not be needed.
 
Thanks for that. The builder and I have managed to get the cable in today. It's a 25mm swa cable and it goes behind a stud wall and then up into the ceiling and then back down into the room where the CU is situated. In this case will the miniature circuit breaker not suffice? Thanks
 
Thanks for that. The builder and I have managed to get the cable in today. It's a 25mm swa cable and it goes behind a stud wall and then up into the ceiling and then back down into the room where the CU is situated. In this case will the miniature circuit breaker not suffice? Thanks
How is your electrician going to inspect this cable? From what you have described, much of it is concealed. It would have been a better idea to assist your electrician in pulling it through, rather than the builder.
 
Thanks for that. The builder and I have managed to get the cable in today. It's a 25mm swa cable and it goes behind a stud wall and then up into the ceiling and then back down into the room where the CU is situated. In this case will the miniature circuit breaker not suffice? Thanks

Hopefully you've left plenty of working room for the electrician to work on the cable an dfit the correct glands to the end of it. You can't just leave an SWA that size sticking out of a stud wall and expect someone to be able to terminate it into the back of an enclosure.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Greater Manchester

Thread Information

Title
100amp Isolator switch required
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
47
Unsolved
--

Advert

Thread statistics

Created
Building advice,
Last reply from
davesparks,
Replies
47
Views
6,021

Advert

Back
Top