Discuss 100Ma Rcd main switch On TPN board in the UK Electrical Forum area at ElectriciansForums.net
hasel5
Got a quick question for you
Been to a dilapidation job today and have the following
TNS-C 100A supply in a Build from 2008 with a 12 way TPN board
Main switch is A 100A 100 MA 4 pole RCD
No 30 MA RCD protection to any outgoing circuits.
So if any circuit has a earth fault whole board goes out lol
Thinking as coding as a C3 on the report
Any thoughts
Regards Nick
Have you enquired as to whether it suffers nuisance tripping. I probably wouldn't Code it at all.
Would fault protection to all circuits comply without it, take it away you will lose the protection it offers. I would comment that additional 30ma protection isn't provided where it may be required or that there is no division of circuits but generally I would not comment on the latter
Thinking 2008 being start of 17th so maybe cables buried in walls with no earthed metallic protection is a possible Plus socket outlets ?
what's the earthing system? if it's TT that may be a reason for the 100mA RCD.
An office block probably shouldn't have a 100mA main switch fitted as disruption of power can be a big problem for servers etc. I would just put it as a comment of the installation as its not against any regs so couldn't really see it being a code 3
Reply to 100Ma Rcd main switch On TPN board in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys, Looking for some options to provide surge protection to a 100a TPN sub main to be wired 60m from the origin Im currently looking at...
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
4K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...