i have a spare 10mm cable under my kitchen cabinets which i ran in ages ago intending to use it for power outside, however i changed my mind and used 16mm instead. so was thinking of putting all appliances on 10mm radial with fcu's.
can anyone think why this would be a bad idea ?
cheers
More copper is always better, although you'll need a JB to break it out into something that will fit into the terminals. Options include drop it to 4mm² or make a lollipop ring using 2.5, leaving the joint accessible for testing.
I suspect you will end up with a "lollipop" arrangement of a junction box and a ring of 2.5mm for the FCUs and/or 13A sockets.
[automerge]1601976346[/automerge]
Ah, Lucien just beat me to it!
[automerge]1601976472[/automerge]
As Lucien also points out, I'm not sure you get maintenance-free boxes taking 10mm size cable, so you will need something accessible. A deep back-box and blanking plate is one way to hide some DIN rail terminals or similar.
Any other ides for joints?
Lollipop ring, I like the sound of that!
There’s plenty of junction boxes available so that ain’t a issue
[automerge]1601976912[/automerge]
what size breaker ?
If it is feeding 4mm radial or 2.5mm ring then 32A B would be the norm. But it would also depend on the Zs at that point and, just possibly, the overall length/voltage drop. But at 10mm feed you would have a crazy length to see that as an issue in most houses!
[automerge]1601977457[/automerge]
Of course, it also needs RCD protection, so either RCBO or take the MCB off an existing RCD.
Alternatively,
Use it to feed a small distribution board in the kitchen
Feed from there to each appliance on a separate 16A radial.
Small kitchen CU.
I'm not keen on extra DB's, when not needed, but, compared with a lollipop on a 10mm.....good way.
Fair bit of external load for a 16mm. How many hot tubs?;)
10mm into a 32a JB under the units , 2.5mm ring coming off of that JB to feed the kitchen sockets / appliances etc off of a 32a mcb
Small kitchen CU.
Yeah I know!
Small shed CU
Power to summerhouse
And if I ever get it built garden studio
And maybe one day a hot tub
[automerge]1601992038[/automerge]
Small kitchen CU.
Reply to 10mm radial ? in the UK Electrical Forum area at ElectriciansForums.net
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...