i have a spare 10mm cable under my kitchen cabinets which i ran in ages ago intending to use it for power outside, however i changed my mind and used 16mm instead. so was thinking of putting all appliances on 10mm radial with fcu's.

can anyone think why this would be a bad idea ?

cheers
 
More copper is always better, although you'll need a JB to break it out into something that will fit into the terminals. Options include drop it to 4mm² or make a lollipop ring using 2.5, leaving the joint accessible for testing.
 
I suspect you will end up with a "lollipop" arrangement of a junction box and a ring of 2.5mm for the FCUs and/or 13A sockets.
[automerge]1601976346[/automerge]
Ah, Lucien just beat me to it!
[automerge]1601976472[/automerge]
As Lucien also points out, I'm not sure you get maintenance-free boxes taking 10mm size cable, so you will need something accessible. A deep back-box and blanking plate is one way to hide some DIN rail terminals or similar.

Any other ides for joints?
 
Last edited:
Lollipop ring, I like the sound of that!
There’s plenty of junction boxes available so that ain’t a issue
[automerge]1601976912[/automerge]
what size breaker ?
 
Last edited:
If it is feeding 4mm radial or 2.5mm ring then 32A B would be the norm. But it would also depend on the Zs at that point and, just possibly, the overall length/voltage drop. But at 10mm feed you would have a crazy length to see that as an issue in most houses!
[automerge]1601977457[/automerge]
Of course, it also needs RCD protection, so either RCBO or take the MCB off an existing RCD.
 
Last edited:
Alternatively,
Use it to feed a small distribution board in the kitchen
Feed from there to each appliance on a separate 16A radial.
 
Small kitchen CU.
I'm not keen on extra DB's, when not needed, but, compared with a lollipop on a 10mm.....good way.
Fair bit of external load for a 16mm. How many hot tubs?;)
 
10mm into a 32a JB under the units , 2.5mm ring coming off of that JB to feed the kitchen sockets / appliances etc off of a 32a mcb
 
Small kitchen CU.
I'm not keen on extra DB's, when not needed, but, compared with a lollipop on a 10mm.....good way.
Fair bit of external load for a 16mm. How many hot tubs?;)
Yeah I know!
Small shed CU
Power to summerhouse
And if I ever get it built garden studio
And maybe one day a hot tub
[automerge]1601992038[/automerge]
Small kitchen CU.
I'm not keen on extra DB's, when not needed, but, compared with a lollipop on a 10mm.....good way.
Fair bit of external load for a 16mm. How many hot tubs?;)
 
Last edited:

Reply to 10mm radial ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
416
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
242
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
786
Hello all, Trained years ago, not done much for about a decade but I've been asked by a friend to add 5x double sockets into an industrial unit...
Replies
10
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock