Thankyou just bored on a Wednesday night, only thing to be wary of if you choose a Switchfuse for the front end then do ask for motor rated fuses 'Gm' or it will come with 'Gg' general use, sometimes they will supply as extra's leaving the general fuses inside for your stock.
 
I have time on my side lickily. I need to power the submain and then have time to sort the tranny supplies.
I will talk to manufacturer in the morning and go from there.
Thanks again, Ill post back how I get on.
Thankyou just bored on a Wednesday night, only thing to be wary of if you choose a Switchfuse for the front end then do ask for motor rated fuses 'Gm' or it will come with 'Gg' general use, sometimes they will supply as extra's leaving the general fuses inside for your stock.
 
So this tx is used to provide power for control circuits and heaters? No tool use?

Using a CTE tx to supply control voltage to panels causes all sorts of problems fault finding when something goes wrong.
 
Its been a long time since I have tested anything 110volts fed from a transformer, but correct me if i am wrong but don't the transformer put out 55volts on both legs ? and therefore you need to double pole everything ?
 
Its been a long time since I have tested anything 110volts fed from a transformer, but correct me if i am wrong but don't the transformer put out 55volts on both legs ? and therefore you need to double pole everything ?

If it's a CT transformer. Daz
 