M

morph

again would sincerely appreciate a bitof help

have a client who wants a mix of stuff doing all in small numbers not really my normal work but have splashed out on a seward 250 to accomadate him and having a few issues on a coulpe of things namely 110 v transformers

could some one please explain how i should test it , i would think its class 1 but i do not get a continuity reading , is it beacuse its isolated from the earth
really would appreaciate a step by step on the 110 transformer
thanks
 
If it is one of the yellow site transformers, they are fully insulated and class 2. The primary earth (3 pin plug site) is directly connected to the secondary centre pint.
You can test earth continuity from the three pin plug to the yellow outlet. You can also perform insulation test ( on 250v ) primary and secondary to each other. Apart from a thorough visual, that is it.
 
yes it is the yellow 110 v box type, on the transformer it has a sticker stating it must be earthed so i thought it to be class 1
how would i do a I/R test primary and secondary?
if i plug the 3 pin plug from the transformer in to tester i could I/R the primary ,
would i then plug a comando socket in to the transformer with an iec plug in to tester and then I/R the secondary?
thanks for your help
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
110v transformers
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
morph,
Last reply from
morph,
Replies
2
Views
5,450

Advert

Back
Top