John-

~
Jan 13, 2019
198
42
103
Uk
Hi Re the above on page 295 of the 18th Ed. regs, it states that for prevention of fire from a short circuit...

One of these areas is a device that protects against short circuit should disconnect within 0.3 seconds when a power increase of 60W (2.5A) occurs.

I have looked at a few disconnection device types Current Characteristics graphs, and i don't seem to be able to find a device that meets this. So to save a bit of time looking through more of these graphs on line, what are people using please?

Maybe the converter has some sort of protection inbuilt, it is a Robus device, so reasonably reputable i think?

I have an example at home of a SELV device supplying several 24v LED strips. The converter is rated at a max output 200w 8.4A. My design current is slightly below 5A so i put a thermal trip in rated at 5A - just to protect the 1.5mm flex cable really. But since reading the regs, and doing the math it seems the device i am using will no way comply to this 0.3s disconnection time (for prevention of fire). My device with a load of 8.3A will disconnect in about 12 seconds and this is not an inrush 2.5A / 60w so is only good for overload. This is my device: -

https://docs-emea.rs-online.com/webdocs/1225/0900766b8122539e.pdf

And I thought i was being clever by protecting the cable and the output, not clever enough i guess.


Thanks

John
 
Are both live conductors uninsulated?
 
  • Like
Reactions: John-
No. I assumed that only 715.422.107.1 applied to those. So are you saying then that .2 also applies to uninsulated conductors only?

:oops:
 
Last edited:
Pretty certain Reg 715.422.107 only applies where both secondary conductors are uninsulated and Reg 715.422.107.2 refers to the device providing the fire risk protection as required by the first Reg. If your system is all insulated including all terminations then so long as your driver/power supply complies to a standard in Reg 715.414 then it should be fine as the driver/power supply should incorporate inherent and non inherent protection.
 
  • Informative
Reactions: John-
If your Ib, In and Iz are in order then surely when a short circuit occurs it will meet the 0.3 second disconnection time (0.1s tn systems)
 
If your Ib, In and Iz are in order then surely when a short circuit occurs it will meet the 0.3 second disconnection time (0.1s tn systems)
This is for extra low voltage side, not the low voltage side. The low voltage side will not be the same current, i guess by a factor of ten give or take losses and the like.
 
  • Like
Reactions: stantheman

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk

Thread Information

Title
18th Ed. 715.422.107.2 Extra Low Voltage Lighting Question
Prefix
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
John-,
Last reply from
John-,
Replies
5
Views
1,467

Advert