It should be at least SPSN, if not DP which is what I originally said, because leaving a N-E fault present is short sighted in my opinion, which is what the vast majority of RCBOs do.
 
It’s all very well if the circuit requires RCD protection , if it doesn’t as stated above a N-E fault would still go undetected, should we be installing sub main supplies in SWA with rcd protection in case there is a N-E fault. Think of the distription due to discrimination this would inflict
 
I did not say you said that either , I suggest you re-read my post. What is incomprehensible about it and I will try to elaborate for you.

What you are saying is that all RCBO’s (in your opinion and not “should be “ Double pole . What I am trying putting across ,is why do you feel this should only be limited to RCD protected circuits . N-E faults would go undetected on most other circuits where RCD protection is not required
 
because if you get a N-E fault this will of course trip the up front SP RCBO device, however by being SP will leave the N-E fault still present.
Now if this was a farm or agricultural install this will also trip the front 300mA RCD required for fire protection, with no means of being to isolate the fault, at least a (SPSN) single pole switched Neutral would Isolate the N-E fault.
This should have been designed in from the get go, even for domestic where a SP RCBO still would leave a N-E fault present.
It would be ---- poor design to have a upfront 300mA rcd with a SP rcbo down stream . I totally agree
 
This is ridiculous. Given what is in the Beama guidance why have so few of the other manufacturers bothered changing their products? It is so fricking shoddy that such a big change is introduced, has been in force for two months, and yet suitable products are not available from all manufacturers of units for the domestic market. What a load of boll***s.
 
Correct me if I’m wrong, but up to a couple of years ago there very few availability DP or SPSN RCBO’s about anyway. Recall one the only available ones from that guy who assembled his own CU products, SBS or something like that.

Now we have these new regs, where these manufacturers have been on the panel, are there’s still sparse availability.

Slightly different subject, but same point £205 for a 6A RCBO/AFDD. Really, see a lot of them going in.
 
So anyone have any ideas on where we stand if we want to add another circuit to an existing consumer unit.

Presumably if I want to add a 32A MCB to a dual RCD consumer unit with 63A RCCB's (lets say for arguments sake they both have a 32,16 and 6A MCB on), I'm also going to have to persuade the customer that I need to upgrade the RCCB to 100A. That's if its even possible to source one for some of the consumer units of course!
 
I read it as the rcd/rccb needs to be equal to or greater than main fuse but diversity can still be applied downstream of them? I am also on some heavy duty painkillers right now.....so could be talking absolute b@&&ocks.....as even with 100a rcd/rccb some consumer total circuits downstream would still be greater than 100a?..........sod it rcbos all the way :)
 
I think if the manufacturer specifies the RCD must be equal or greater than the fuse, then that's what needs doing. We used to have leeway with design to ensure the RCD wasn't overloaded, but now we shall do as we are told :) .
 
sorry if this is duplicated - I had trouble posting it.

I only tend to read through the forum once a week. Not to be able to take diversity into account w.r.t. RCD rating is, in my opinion, quite ridiculous. Very few 32A RFCs ever get more than maybe a 3 kW fan heater and a few other low power items running at the same time - say 15A total - so maybe we should be fitting 20A MCBs to RFCs - especially upstairs RFCs. Kitchen and utility circuits usually supply more current, but even then 20A would normally suffice (apart from cooker and shower). Maybe this approach would be better that replacing 20A RCDs with 100A ones? As another previous post said, this requirement undermines the whole issue of diversity.

I strongly suspect that this RCD nonsence (and the AFDD one!) is manufacturer profit driven. Don't forget that "BEAMA is a member association that represents manufacturers of electrical infrastructure products and systems", it is NOT a safety organisation. It represents its manufacturing members and promotes their financial and other interests. It is a manufacturers "friendly society" or club.

The IET seems to have somewhat lost the plot with the buggy and imprecise "recommendations" in the 18th Ed. Maybe they should hand the job over to CIBSE as someone above suggested. I don't know if they would be better, but IET seems to have lost the art of practical electrical common sense.

I despair that red-tape is starting to overwhelm the comon good in an increasingly expensive "throw away and don't attempt to repair" society.
 
I get up to the point in the regs with the use of RCD's/RCBO's for sockets to protect against faulty equipment and for the greater risk areas eg bathrooms outdoors swimming pools etc from then onwards the regs are being written to protect the idiots eg metal stud, cables in walls domestic lighting circuits AFPD's not saying that they are bad things. If the installation is designed and constructed using approved materials together with good sound workmanship the extra protection should not be needed the trusted fuses and MCB's served well for many years.
 
I get up to the point in the regs with the use of RCD's/RCBO's for sockets to protect against faulty equipment and for the greater risk areas eg bathrooms outdoors swimming pools etc from then onwards the regs are being written to protect the idiots eg metal stud, cables in walls domestic lighting circuits AFPD's not saying that they are bad things. If the installation is designed and constructed using approved materials together with good sound workmanship the extra protection should not be needed the trusted fuses and MCB's served well for many years.

Thats ok until the end users get involved, i.e. human beings, then everything goes swivel.
 

Reply to 18th Edition Compliant Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
226
Hi everyone. I currently have a level 2 diploma, Part P and 18th edition. Can I carry out a consumer unit change if I work for myself privately?
Replies
4
Views
975
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
778
having failed my first attempt at 18th edition exam, does anyone have any tips and tricks on how to study for the exam? being that there is a...
Replies
8
Views
795

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock