Historically we have used diversity of the final circuits to ensure that the rccb is not overloaded.
Now it seems we can not rely solely upon diversity of the final circuits downstream of the rccb and overload protection must be ensured by other means like having the upfront ocpd rated lower or equal to the rccb and main switch or ensure that the final circuits added are not greater than the rccb and ensuing manufacturers instructions are complied with.
I know with Hager they have taken the approach of fitting 2x 100amp rccb’s (Also now type A) in their dual rcd consumer units so obviously they intend to ensure that their rccb’s are not overloaded and have defaulted to use 100amp devices.
This is certainly the guidance also given by my companies scheme provider.
And the correct guidance.