Ive never seen or used this method ,but it would work! ,must be foregn i think ,i always use the 3 plate method ,live at one end ,switch wire at the other,neutrals at the light ,never at the swich,so i wouldnt recomewnd doing this ,its strange
atvbitwww
 
I take my 3 core from switch to switch but when I first started 3 years ago the spark I worked with taught me to take my 3 cores from each switch to the ceiling rose and crimp it through in the rose.
 
live and neutral to the light 3 plate method
run 3 core between the switches ,via the light to save cable ,leave the strappers intact ,cut the "red" and conect one end to live and the other is the switch wire ,
thats how i do it if using 3core ,i am proberbly going to be told its wrong ,but i dont know that other method
this thread could get interesting !

live and neutral to the light 3 plate method
run 3 core between the switches ,via the light to save cable ,leave the strappers intact ,cut the "red" and connect one end to live and the other is the switch wire ,
thats how i do it if using 3core ,i am proberbly going to be told its wrong ,but i dont know that other method
this thread could get interesting !
 
Last edited by a moderator:
Permanent live in rose and s/w at switch. Take one 3 core cable between the 2 switches, That's how I do it.
 
Thats what i know as the convertion method,usefull if converting one way to two way,uses more cable and is a bit more time consuming ,but nothing wrong with it ,only the crimp in the cswitch box ,which some consider bad practice for new work ,i dont mind which way its done
atvbitwww
 
where do you pick your common up from then ,i asume you run a 2 core down from the ceiling rose?
 
Old colours I know but like this
<a href="http://www.flickr.com/photos/7707130@N06/2310515723/" title="tw4 by [email protected], on Flickr"><img src="http://farm3.static.flickr.com/2084/2310515723_b8cb9afbc4.jpg" width="335" height="425" alt="tw4" /></a>

where do you pick your common up from then ,i asume you run a 2 core down from the ceiling rose?
Yeah, off your switch wire
 
Last edited by a moderator:
No, at the other end you will just have a 3 core so common (same as at your other switch obviously) and then an earth and two more cores which are strappers
 
Sorry not disagreeing ,but cant understand it ,i was shown for this method take a two core from the rose ,join the live to the red in the three core and swichwire in the common terminal at one swich and connect the other again with red in the common and strappers in the l1 and l2,obviouslly this means a crimp or connectior in the switch box ,cant quite see where you get your supply from ,i must be confused by what you meen ,
 
L/N/E to rose connect T/E (that will drop down to switch 1), one core (brown) to loop terminals of rose the other core (blue sleeved brown) to Switch return terminal of rose . This T/E at switch 1 will now connect to L1 & L2.
Connect 3c/e at switch 1 to common L1 & L2 terminals & do the same at switch 2.

Make any more sense to you?
As you say RR this practice is or was known as the conversion method.


Wait untill you come across multiple runs of T/E used for 2way switching via terminal strip enclosed in a JB4 hidden away in a ceiling & customer wants an intermediate fitting :eek:....deep joy....bring on the conversion method:D
 
Last edited by a moderator:
Got it ,is my original method of taking 3core via the light not right now ,and what about the method luke posted ,whats that all about
atvbithwww
 
Hi Mac
I think thats whats known as the conversion method ,i was never sure how to do it as i was shown the conector method mentioned earlier ,all the wiring i did as an apprentice was in conduit ,so its different again ,done plenty since in tae ,think i will start doing it like this in the future ,thanks for your posts ,i love learning new stuff,
atvbitwww
 

Reply to 2 way switching in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock