Hi everyone, I'm currently upgrading my workshop and before I get quotes for the electrics I'd like to understand it better myself. If I want 6 sockets from a ring mains circuit can I spur off an existing socket to a 20a DP switch and run the 6 sockets from that? It's unlikely the load will exceed 4kw, there will be an electric heater running, as well as a kettle, microwave and occasional use of electric saw etc. Or would I be better off running 3 sockets each from two separate 13a FCU switches spurred off two different sockets on the ring circuit . Any advice would be appreciated many thanks.
 
no you can't spur off a ring without fusing down. for the load you anticipate, you need to extend the ring. i.e. split at convenient socket and loop round the workshop, making all of the sockets on the ring. should end up with something like this. 2 existing cables and 2 new cables .
 

Attachments

  • rfcextend.jpg
    rfcextend.jpg
    237.8 KB · Views: 59
Last edited:
no you can't spur off a ring without fusing down. for the load you anticipate, you need to extend the ring. i.e. split at convenient socket and loop round the workshop, making all of the sockets on the ring. should end up with something like this. 2 existing cables and 2 new cables .
I see many thanks for the reply telectrix.
 
One final though, presumably you don't actually need an isolation switch (or emergency stop) for any other workshop safety reason?

If it is just for hobby stuff without any seriously intimidating equipment then just go with the ring extension. Otherwise if you really need some means to isolate the whole area you would be better with a separate 4mm radial from the CU just to feed the 6 sockets via a local isolation switch.
 
One final though, presumably you don't actually need an isolation switch (or emergency stop) for any other workshop safety reason?

If it is just for hobby stuff without any seriously intimidating equipment then just go with the ring extension. Otherwise if you really need some means to isolate the whole area you would be better with a separate 4mm radial from the CU just to feed the 6 sockets.
My understanding was that you could only spur off to multiple sockets if you had a fused switch coming off the ring first. And because I planned to be able to run an electric heater, kettle and microwave at the same time for example I presumed that would blow a 13a fuse, hence why I presumed a 20a DP switch could just be used instead. I'll be getting a professional round at some point but would be handy to know the options beforehand. Also the CU is a fair distance from my workshop hence why I thought the spur would be easiest/cheapest option!
 
a 20A D/P switch is no good. it's not fused. you could fit a 20A MCB in a small enclosure to feed a spur, but for the load you mention,better as a ring extension (you only need to access a local existing socket, no need to go back to CU) so you have a 32A capacity. the 32A MCB will allow small overloads for short time periods without problems.
 
My understanding was that you could only spur off to multiple sockets if you had a fused switch coming off the ring first. And because I planned to be able to run an electric heater, kettle and microwave at the same time for example I presumed that would blow a 13a fuse, hence why I presumed a 20a DP switch could just be used instead. I'll be getting a professional round at some point but would be handy to know the options beforehand. Also the CU is a fair distance from my workshop hence why I thought the spur would be easiest/cheapest option!
Extending the ring maybe your cheapest and easiest option but if you intend to use the workshop on a regular basis with multiple equipment, then personally, if its an option, I would seriously consider a separate supply from the CU.
 
I would look at running a separate circuit for your workshop. Last thing you want is something tripping the power and taking out a circuit in the house as well.
 
I would look at running a separate circuit for your workshop. Last thing you want is something tripping the power and taking out a circuit in the house as well.
Many thanks for the reply, out of interest if I extended the ring circuit would that mean the max possible amp on the circuit would be 32A before it trips?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
g40
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
20a DP switch spur for 6 sockets
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33
Unsolved
--

Advert

Thread statistics

Created
G100917,
Last reply from
telectrix,
Replies
33
Views
4,360

Advert

Back
Top