I have been asked to carry out an install, it is a mobile dog grooming van, and my customer has asked my if I will need to certify it, I have read through the BRB, and my understanding is that It wont. But I want to make sure, the van will have a consumer fitted and a commando socket for the main feed in from the customers property via an extension lead ( I know), the consumer unit will have a 30mA RCD mainswitch, but any testing i carry out will have different results depending on his customers earthing arrangements. Am I right?

Kind regards to all who reply

Chris Hughes
 
yes you will have to test it its a mobile installation section 717 BRB
When testing use the long lead method for R2 reading and do all your dead testing and record the result. On the certificate make note its mobile and adiquacy of earthin cannot be garenteed.
As you said the ZE will vary when the van is moving so prove your RCD treat the van as a TT sytem
 
Thanks for that scotsparky, but would it not also come under 721. I know it relates to caravans, I think you are right about the testing as is though
 
I have been asked to carry out an install, it is a mobile dog grooming van, and my customer has asked my if I will need to certify it, I have read through the BRB, and my understanding is that It wont. But I want to make sure, the van will have a consumer fitted and a commando socket for the main feed in from the customers property via an extension lead ( I know), the consumer unit will have a 30mA RCD mainswitch, but any testing i carry out will have different results depending on his customers earthing arrangements. Am I right?

Kind regards to all who reply

Chris Hughes

Can see a problem with the 30mA RCD in that if they go to a house which is fitted with an RCD there will be no discrimination between them.
 
Thats the problem, the houses he goes to, he cant garentee the quality of the customers c/u, so the only thing i could suggest would be to plug it into an rcd adapter socket to start with, what do you reckon
 
Depending upon what the loading is how about fitting a RCD DB supplied via an invertor supplied by a seperate set of batteries which can be charged by plugging in a rectifer unit when at customers house.

On second thoughts might cost a bit more than what your client wants to spend.
 
The best way is probably some sort of separation by way of an isolating transformer.

I'm rather concerned that you thought you 'wouldn't need to certify it' even after reading 'the BRB'.

This type of installation has the potential to become very dangerous, not least when plugging into TN-C-S earthing systems etc. and therefore careful consideration should be given to the final design!

Guidance Note 7 is a must-read for this type of installation.
 
I agree - convert it to an IT system in accordance with 717.411.6.2 - the mobile dog groomer is unlikely to want to have to start driving earth stakes into customers' flowerbeds every time they park up on a driveway.
As regards testing obviously do the dead tests but there's not a lot of point doing live testing because as mentioned it's going to be different at every property it's plugged into.
 
need me eyes testing. read thread as 230 electricians in a van. was just about to phone guinness book of records.
 