Can anyone tell me if you can run 240v and 24v in a multicore swa i think i am right in saying if the cable rating of the 24v and 240v are the same then you can,maybe best to clearly label thecable voltages on the cores ?
 
Provided there won't be any adverse effects from magnetism caused by the 230v (515.2) it should be ok if the cores are insulated to the highest voltage, as per 528.1.
 
I would say it's bad practice to have ELV and LV in the same cable. If there's nothing about it in the rules then I suppose you could do it but it might be problematic with two systems sharing the same CPC for example.
 