does having two circuits travelling down one swa directly condradict a reg.?
Circuits in question are 2 63A submain down 1x 4c 16mm swa
 
I do not believe there is any contravention there, two circuits in the same containment, just a little more difficult to separate. The armour would need to be suitable as a cpc for the worst case.
 
No it is fine, if it was conduit you wouldn't pose the question it is really no different.
 
Interesting one. That figure would you use for grouping factors?
 
I suppose you could use the 3 phase figure from the tables.
 
Hi why would you need to group, its already rated assuming all conductors loaded?

You have two single phase supplies going to different submains, in a 4 core cable.
Do you not think grouping should apply?
 
Think he means 2 x single phase supplies in the one SWA.

Yes I know, just if it's possible take all 3 from the source or you could end up with 2 loaded up phases.

2 of 3 phase boards populated as single phase supplies.

Like I said no specific info but thought I'd ask.
 
You have two single phase supplies going to different submains, in a 4 core cable.
Do you not think grouping should apply?

Hi

In single phase what goes up must come down, so other than the proximity effect the CCC will be similar.
 