Discuss 2x supplies down swa in the UK Electrical Forum area at ElectriciansForums.net
Interesting one. That figure would you use for grouping factors?
I suppose you could use the 3 phase figure from the tables.
Hi why would you need to group, its already rated assuming all conductors loaded?
You have two single phase supplies going to different submains, in a 4 core cable.
Do you not think grouping should apply?
Think he means 2 x single phase supplies in the one SWA.
Yes I know, just if it's possible take all 3 from the source or you could end up with 2 loaded up phases.
2 of 3 phase boards populated as single phase supplies.
Like I said no specific info but thought I'd ask.