But the OP said three single phase supplies from 1 3 phase supply, he didn't say one phase for all three supplies you silly Northerner lolCan't resist any longer!
3 single phase 15kW heaters wired with 3P plugs on Brown, plugged into these three sockets..............

Can't resist any longer!
3 single phase 15kW heaters wired with 3P plugs on Brown, plugged into these three sockets..............
But the OP said three single phase supplies from 1 3 phase supply, he didn't say one phase for all three supplies you silly Northerner lol
No don't do it, we have lost too many good men to that trade already LOLI'm going to become a plumber.
Well yes, but not 3 times larger which is where the thread seemed to be going at one time, to answer the OP=no problem providing the load for each phase does not exceed the protective device for that phase.The end result is the neutral conductor should be designed to carry the most onerous current that could flow in it. Hence, under a pure resistive load condition, the neutral conductor needs to be the same size as the line conductor.