Can't resist any longer! :-)

3 single phase 15kW heaters wired with 3P plugs on Brown, plugged into these three sockets..............
But the OP said three single phase supplies from 1 3 phase supply, he didn't say one phase for all three supplies you silly Northerner lol
 
But the OP said three single phase supplies from 1 3 phase supply, he didn't say one phase for all three supplies you silly Northerner lol

Damn you smart arse southerner, BUT if it was wired in a weird way....

I'm going to become a plumber.
 
But that would then be exceeding the capacity of the equipment and a better design required, and it is hypothetical as it is not what the OP mentioned haha

- - - Updated - - -

I'm going to become a plumber.
No don't do it, we have lost too many good men to that trade already LOL
 
OK. assume all 3 phases pull the same. neutral current =0.

take a possible scenario. L1 =63A, L2 = 10A, L3 =10A, N current will be around 53A. and you'll get similar results for any combinations. N current will never exceed 63A.
 
The end result is the neutral conductor should be designed to carry the most onerous current that could flow in it. Hence, under a pure resistive load condition, the neutral conductor needs to be the same size as the line conductor.
 
The end result is the neutral conductor should be designed to carry the most onerous current that could flow in it. Hence, under a pure resistive load condition, the neutral conductor needs to be the same size as the line conductor.
Well yes, but not 3 times larger which is where the thread seemed to be going at one time, to answer the OP=no problem providing the load for each phase does not exceed the protective device for that phase.

- - - Updated - - -

Yes hooray for Tel, but me and Diilb did try to tell everyone LOL
 
this thread =



GFP.png

.............
 