So do you think manufacturers supply plant worth millions and let the buyer just switch it on?

Commissioning can take days or even weeks on some plant
no i dont think that. you just set to FLC end of story.
yes darkwood you are correct, i didnt include 25% to star/delta what can i say im a fool, how can i recover from this, yes its the end ,suicide is the only answer, goodbye cruel world.
 
125% comes from the days of magnetic dashpot O/L’s. It’s a hangover that just won’t go away.
 
What d'you mean Tony? Are you saying these electronic motor protection relays haven't got teeny little dashpots inside? I've been ever so careful to keep them the right way up all the time...

Pepparz: Centrifugal blowers - maximum mechanical load normally when flow is completely unrestricted. If you've run it up like that in the shop, you know what the maximum line current will be, ever. If it was 75% flc then why set higher?
 