BroadReach

Hi All

I would appreciate your help with the following.

I am familiar with standard calculations such as calculating the current draw on a three phase heater battery when the loads are balanced across the three phases. I have recently come across some equipment where it appears the heater battery has been deliberately designed with a load imbalance. I believe this is to enable the manufacturer to use their standard elements to produce alternate heat outputs for special purposes.

The heater is as follows:

2 off 21 Ohm heaters and 1 off 27 Ohm heater wired to a 400V 3 phase supply in star formation with floating centre point.

Now I know that 3 off 21 Ohm heaters wired this way would result in about 10.9A/ph and 7.5kW heat
and 3 off 27 Ohm heaters wired this way would result in about 8.7A/ph and 6kW heat

How would I calculate the current draw and heat output of the hybrid heater battery?

Any help appreciated
 
I have been thinking about this since Friday and am asking for pointers to work it out rather than just an answer to this example.

OK so if there was a neutral to the star point then it would be easy as the phase to neutral voltage on a 400V 3 phase system is 230V and I could then use Ohms law to work it out. In my example above the answer would be 2.5 + 2.5 + 2 = 7kW with 10.9A down two phases and 8.7A down the third with a neutral current of 2.2A.

What I am thinking is how to work out the phase to centre point voltage as with no neutral this will float away from Zero I believe. Once I know this then I think Ohms law is my friend again?

Edited to add:

Perhaps another way is to work out the current draw on each phase and then calculate the power from there?

Problem is I know how to use a vector diagram to work out neutral current in an unbalanced TP&N system but cannot visualise how to use one to work out either of the above in an unbalanced TP system.
 
Last edited by a moderator:
I'm not an electrician
I'm not a student looking for an answer to my homework
I'm not a DIYer looking to do something on the cheap

I am a Mechanical Engineer who would like a better understanding of the electrical bits of the kit I sell/specify.

Any help appreciated.
 
Just finished the Observer and Mail crosswords.

1 across: To gain knowledge (3)
2 down: Singular thing (3)
3 across: A maker of things (12)

Answer will be in tomorrows paper
 
Just finished the Observer and Mail crosswords.

1 across: To gain knowledge (3) ASK
2 down: Singular thing (3) THE
3 across: A maker of things (12) MANUFACTURER

Answer will be in tomorrows paper


Well thanks.

Manufacturer says 10.9A/ph. On questioning this they say this is the MAXIMUM current draw that will occur on any one phase and will not elaborate further.

I am not convinced this figure is actually correct anyway, gut feeling says it could be less.

Do you, or anyone else, want to give me any help or pointers on this?

Edit:
Beaten to the crossword, too slow typing
 
The average current you've been given is for 440V, which ties with the "max" he quoted. One phase current will be a bit lower than the other two by 6.25%
 
Last edited by a moderator: