3 phase motor current rating
J
Jempe1012
Hi
can Someone please show me how I can work out the current rating of a 3phase motor from its kw rating?
Singel phase is just kw/watts but I know 3phase is defferent.
Cheers
I = P/ (sq.rt.3. x V x PF)
so e.g. a 5kw motor
I = 5000/ (1.732 x 400 x 0.8) assuming a 3 phase voltage of 400 and a pf of 0.8
I = 5000/(554.25)
I = 9.02A
I cheat and drop the figures in to a spreadsheet.
But he’s the formula for you:
A=((KW/3)/(V/√3))*1000
If power factor is known:
A=(((KW/3)/(V/√3))*1000)/cosΦ
If efficiency is known:
A=((((KW/3)/(V/√3))*1000)/cosΦ)/Eff%*100
Once you’ve get a few more posts under your belt I’ll e-mail the spreadsheet to you if you ask. Sorry but I’ve had quite a few newcomers asking for copies in their first post, I wrote it for the benefit of members.
so e.g. a 5kw motor
I = 5000/(554.25)
I = 9.02A
Very helpful thankyou, what do I do if I don't know the power factor I think they just give the motor kw rating?
You can kinda guess the PF as 0.8. This may vary depending on how well loaded the motor is running (pf gets better as load increases) and whether or not it's a high efficiency motor.