Discuss 3 phase motor intermittantly tripping in the Industrial Electricians' Talk area at ElectriciansForums.net

Reaction score
0
I have got a 3 phase motor running a conveyor belt, every couple of days it will trip the overload. I have tested the motor, windings are ok, not drawing excessive current, good insulation resistance. It has a brake mounted on it but this seems to be releasing ok.
Motor does get a bit hotter than the 2 conveyor motors next to it.
any ideas
 
What is the flc of the motor?
What are the overloads set at?
How it it wired DOL or SD
How is the motor configured Star or Delta?
 
Intermittent problems are the hardest to find. could be as said above.
Do the basic things first
Check the belt runs freely no stiff bearings or badly tracked belts.
Clean the fan, cowl, and motor casing so it can cool correctly.
Check condition of any remote isolator and the actual contactor loose, dirty or pitted contacts can cause intermittent phasing and overload. Also check and test cable condition.
Use a clamp meter to check the current draw each phase.
Do you know if its tripping on start up or after its been running for a while?
 
More info required. As per Pete's questions, how's it wired, YD, DOL or is there a drive?
 
What material are you conveying? If the environment is dusty or damp, or the faulting conveyor is used more than the others, you may have to up the PPM on that asset. Overloads generally set at 5/8 FLC or 65% ish, if its already been cranked up there may be much knee work and head scratching.
 
If the current, load, load frequency, and environmental are same as other two motors. You confirmed all wiring. you could be seeing the results of a past problem. Like a previous load issue over heated motor and caused insulation failure, or contractors worn from past problem. Basically I am reminding you to consider, past abuse may have have caused degradation which now presents itself to appear as intermittent problem when it is really an accumulative issue. Ringing it and use a scope may help verify.
 
What material are you conveying? If the environment is dusty or damp, or the faulting conveyor is used more than the others, you may have to up the PPM on that asset. Overloads generally set at 5/8 FLC or 65% ish, if its already been cranked up there may be much knee work and head scratching.

Only if the motor is YD and the overload is in the delta leg.
 
Common practice in the states, and when the cores get too big for fire nuts:
900_zpskofnsoag.jpg


View attachment 35874

View attachment 35875
 
Can we all get back on topic instead of bouncing and rising up off each other, it will only drag the thread off topic and lower the tone, a little appreciation to differing terminologies would help too.
 
Stupid Septics Meg a motor, what next?

Pete, please can we avoid such comments please, calling members stupid for the different international workplace slang is not going to help, it is often taken offensively hence the response you got, can we be a bit more respectful to our new American member.
 
Pete, please can we avoid such comments please, calling members stupid for the different international workplace slang is not going to help, it is often taken offensively hence the response you got, can we be a bit more respectful to our new American member.
Yes OK sorry guys
 

Reply to 3 phase motor intermittantly tripping in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
527
Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...
Replies
2
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock