I set the O/L up to the motor duty in normal running and not the rating + whatever % of the motor this way issues are picked up early doors without major down time as such.....when it trips you know something is making the motor work harder usually the gears haven't been topped up with the slippy stuff.My old engineer used to say..............flc + 10% for o/load setting.
Worked fine until someone put hydraulic oil in the o/load dash pots
Just curious but what do other folk set their motor overloads at. ?
Does anyone actually think about it or just accept what their set at !
I,ve worked in industry quite a lot, and within various factories, and motor overloads have been set from 100% FLC to 130% FLC depending on circumstances but I would say 110% is about the most common I,ve experienced. Trying to get a balance I suppose between protection and nuisance tripping.My old engineer used to say..............flc + 10% for o/load setting.
Worked fine until someone put hydraulic oil in the o/load dash pots
Just curious but what do other folk set their motor overloads at. ?
Does anyone actually think about it or just accept what their set at !
Exactly what I said and do ...this has saved my customers countless down time as I work in the cotton industry a lot and it can wrap around the roll bars and beariings, when it trips I usually have extra available motor power to increase the O/L setting in the short term to overcome the resistance and schedule in a shutdown at convenience.If the motor is under constant load we set the overload according to the normal running current and not the FLA marked on the info plate. For example if a motor has an FLA rating of 33Amps but under normal operating conditions it only draws 26.5Amps we'd set the overload at 26.5 + 10%.
Anything critical would be oversized, electrically and mechanically. I had an 800HP blower motor with smoke coming out of it, the little beauty kept slogging on though. By this point all ancillary staff had been told to leg it out of harms way. The plant controller, charge hand fitter and myself as shift engineer had to stay. Common sense would say leg it, try explaining that in an enquiry in to a plant explosion! “You saved yourself, now there’s the body count to tally.”
The motor wasn’t very well afterwards. To rub salt in the wounds, my shift changed it!
and if left.....cotton and wool can shear through shafts as well.....Exactly what I said and do ...this has saved my customers countless down time as I work in the cotton industry a lot and it can wrap around the roll bars and beariings, when it trips I usually have extra available motor power to increase the O/L setting in the short term to overcome the resistance and schedule in a shutdown at convenience.