duncan, you need to know the current capacity of that 1.5mm cable feeding the motor. assuming it's around 16A, then your MCB needs to be rated less than 16A. bearing in mind that the MCB protects the cable. you would need to use a type C to handle the start up current without tripping, so a 10A would seem appropriate. another point to note, if you are not au fait with 3 phase, is that if the motor runs the wrong way you have your phase rotation incorrect and would then neede to swap any 2 phases at the motor isolator.


Cheers Telectrix. I was aware re turning the phases, thanks - gleaned that from today's research :)

10 amp was my own first thought, but Darkwood suggests 20amp and I think I see where he's coming from in the info he posted in #30.

Darkwood also asked for a pic of the plate and I did take one, just about to get it off my phone and post it here.

Thanks again.
 
IMG_0099.JPGIMG_0103.JPG

These are pictures of the plate and of the flexible cable feeding the motor. The other end goes to the isolator and the feed side is wired from SWA. Not great pictures, but I'm pretty sure the stranded flexible cable is 1.5mm. The neutral (unused) is the core seen wrapped around the bottom.
 
That’s a high current for a 2.2KW 400V motor. At .85 power factor and 90% efficiency I get 4A. Change to 230V it works out as 7A?
As it’s 2[SUP]nd[/SUP] hand it’s obviously worked before. You’ll just have to try it out. It’s the only thing you can do.
 
It was the fact that it had been used before and that it was even pre-wired that nudged me towards agreeing to connect it for him.

Also, he knows the guy in the garage it came from, and has seen it working on several occasions.

I'll definitely let you know how I get on.
 
It was the fact that it had been used before and that it was even pre-wired that nudged me towards agreeing to connect it for him.

Also, he knows the guy in the garage it came from, and has seen it working on several occasions.

I'll definitely let you know how I get on.

Doesn't mean that it's right.
Assumption being one of the 'Mothers of All ???? Ups'

Leave this to Tony!
 
6.4A is wrong for a 2.2KW 400V motor. It’s for a delta connected 230V motor, for 400V you will have to connect it in star.


Tony I'm no expert on motors.

But you are right the 6.4A rating for a 2.2KW 3P motor is for a delta connected 230V supply.

For Star connected, 400v 3P 2.2KW motor the current will be 3.19A.

So a 6A c-type breaker will suffice with 1.5mm cable.
 
Duncan note on your second pic.... SY cable has been utilised to supply motor... but i see the screen has been taped off, make sure you earth the screen as its a possibility if the cable is damage it may become live otherwise, and Note! on my mcb choice, alot of people question why i have picked mcb's alot higher than expected, i cross reference them to manu' guides of mcb's and recommended mcb in relation to motor size.... having said that a 2.2Kw would normally need a 16amp(b) or a 10amp(c); In your case the motor current FLC (full load current) is that of a 3Kw motor hence i have thus given the mcb rating for a 3Kw motor. Following this advice you will eliminate periodic nuisance trips due to inrush.
 

Reply to 3 phase motor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked if I can wire a motor for a car lifter in a domestic garage, however the motor is 3 phase and only single phase is available in...
Replies
5
Views
831
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
802
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
354
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
686

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock