As tony already mentioned your motor plate sounds strange... A 2.2kw would usually be around the 4.8amp, the 6.4 you state is normally akin to a 3kw motor but its possible its none standard.
Going by your 6.4FLC rating then you require a 20A mcb and a type B or C will suffice, as you'll realise its far from the 6amp you suggest, and also you did state the ampage as 6.4 so why suggest a lower rated mcb...(6amp); would you put a 10amp mcb on a 13amp heater??.. if you get my drift , its this that has had people question your background.
 
Hi Mickys86. Thanks for your answer.

Tony did ask a question on the motor and I replied with the information I have.

Honestly. I'm really surprised by some of the reactions on here; questioning my validity as an electrician? I resat my grade card two months ago - the SJIB must be nuts to have given it to me I think.

Here's my story though - for what it's worth. I served my time with an old lad who had a shop in the Morningside area of Edinburgh. We did rewires, domestic alterations, churches, shop-fitting, that sort of thing. I can tear a domestic house apart and put it back together again without a mark. I also learned a good deal about plumbing, joinery, tiling, painting and decorating, etc. I was a DOMESTIC Electrician - that was my game. I eventually took over from my boss and ran the business myself. I know my limitations though; I wouldn't take on industrial work - I subbed that to guys who could do it. I know sparks who work in factories and look after the machinery there - they know their stuff - I wouldn't have a clue, so I don't take on that kind of work.

I then left the trade altogether in a career change which took me into professional football - on the admin. side, I know my limitations in that respect as well. After a number of years - first with the Club, and then as a freelance photographer - I decided to return to the trade last year. Things have changed a bit, but I worked through the books, sat the exam at Select, and had my gradecard renewed by the SJIB.

I'm now picking up where I left off - I don't take on industrial work and I DON'T work with motors, and if that's a hanging offence then I'm sorry. I change sockets, and switches for Mrs. Blogs, I put up light fittings for Mrs. Tuppence-worth. I'm working on an estimate to wire a new build home, and another to revamp a bathroom.

I cam on here because a mate asked me to wire his electric ramp: It came from another garage. Whoever took it apart also supplied it with the control switches, isolator and swa cable still intact. Basically, all I have to do is fix the cable to the surfaces and reattach the SWA gland at the board. But I thought I'd just come on here and check on the breaker. I didn't mean to instigate a war: check my membership details; i never swear, make snide comments or belittle users. I also apportion 'thanks' on as many occasions as I can.

I really admire guys like Tony who are experts in their field, and I have loads of respect for all the guys who swap mathematical formulas on here - they obviously work hard at knowing their game. I'm a domestic electrician, pure and simple - I have no allusions of being more than that. But things have changed a lot since I was last on the tools - I'm getting to grips with it but, honestly, I have neither the need nor the will to start learning about three phase electric motors. The job I'm doing is a one-off for a young mate who's just starting out, I have no intention of adding that sort of work to my jobbing CV

These boards are fantastic though. Most of the time I just come on to glean information. I don't pretend to know it all and these boards have probably saved me hundreds of research hours. Occasionally (as you can see) I also ask a question. But to be berated and belittled for doing so! Why? If you think it's a stupid question then isn't it easier just NOT to say anything. Is there anyone on these boards who doesn't have some aspect of their trade which they're not sure off? My boss used to big me up 'cause I had a deft touch and could 'fish' a cable out of a lathe and plaster ceiling from 15 yards in record time. Have ALL the sparks on here done that? Not that that makes me clever, but it was one of the things I was good at as a domestic spark. On the other hand, I didn't come across many three phase motors in my line of work. Delta and Star!! Last time I looked at that was in college - about 40 years ago.

Anyway, if no one minds too much then I'll continue to use these boards for research, and I might even make a post or two, but I'll make sure I'm qualified enough to know the answer first.

And thanks, again, Micky for your help.
 
check my post 25 you may have missed it while writing all that, these are manufactered mcb guidelines for a 6.4amp motor.
 
check my post 25 you may have missed it while writing all that, these are manufactered mcb guidelines for a 6.4amp motor.

Exactly what I was looking for, Darkwood. Many thanks, and yes, it was a bit stupid to suggest a 6 amp, I don't even know why I did. But I'd spent two and a half hours trying to find the answer myself before putting the question on the board, and my head was spinning with it. :-(

Thanks again, much appreciated :)
 
duncan, you need to know the current capacity of that 1.5mm cable feeding the motor. assuming it's around 16A, then your MCB needs to be rated less than 16A. bearing in mind that the MCB protects the cable. you would need to use a type C to handle the start up current without tripping, so a 10A would seem appropriate. another point to note, if you are not au fait with 3 phase, is that if the motor runs the wrong way you have your phase rotation incorrect and would then neede to swap any 2 phases at the motor isolator.
 
duncan, you need to know the current capacity of that 1.5mm cable feeding the motor. assuming it's around 16A, then your MCB needs to be rated less than 16A. bearing in mind that the MCB protects the cable. you would need to use a type C to handle the start up current without tripping, so a 10A would seem appropriate. another point to note, if you are not au fait with 3 phase, is that if the motor runs the wrong way you have your phase rotation incorrect and would then neede to swap any 2 phases at the motor isolator.
Tel .... the motor and its flex will be protected by an overload device and wont see much more than the overload setting for the motor, the supply to the ramp would at a guess without questioning the install details be a 2.5mm swa covered by a 20(b) mcb..... this will be what is required unless the cable calcs are asking for larger ccc due to install methods.
Duncan...
I suspect the ramp has inverter control hence the strange ampage for motor (delta set up), you should refer to ramp instructions for mcb rating but if not available my suggestion should suffice, be nice if you could post a pic of motor plate or give details of ramp manufacturer.
 
Last edited:
duncan, you need to know the current capacity of that 1.5mm cable feeding the motor. assuming it's around 16A, then your MCB needs to be rated less than 16A. bearing in mind that the MCB protects the cable. you would need to use a type C to handle the start up current without tripping, so a 10A would seem appropriate. another point to note, if you are not au fait with 3 phase, is that if the motor runs the wrong way you have your phase rotation incorrect and would then neede to swap any 2 phases at the motor isolator.


Cheers Telectrix. I was aware re turning the phases, thanks - gleaned that from today's research :)

10 amp was my own first thought, but Darkwood suggests 20amp and I think I see where he's coming from in the info he posted in #30.

Darkwood also asked for a pic of the plate and I did take one, just about to get it off my phone and post it here.

Thanks again.
 
IMG_0099.JPGIMG_0103.JPG

These are pictures of the plate and of the flexible cable feeding the motor. The other end goes to the isolator and the feed side is wired from SWA. Not great pictures, but I'm pretty sure the stranded flexible cable is 1.5mm. The neutral (unused) is the core seen wrapped around the bottom.
 
That’s a high current for a 2.2KW 400V motor. At .85 power factor and 90% efficiency I get 4A. Change to 230V it works out as 7A?
As it’s 2[SUP]nd[/SUP] hand it’s obviously worked before. You’ll just have to try it out. It’s the only thing you can do.
 
It was the fact that it had been used before and that it was even pre-wired that nudged me towards agreeing to connect it for him.

Also, he knows the guy in the garage it came from, and has seen it working on several occasions.

I'll definitely let you know how I get on.
 
It was the fact that it had been used before and that it was even pre-wired that nudged me towards agreeing to connect it for him.

Also, he knows the guy in the garage it came from, and has seen it working on several occasions.

I'll definitely let you know how I get on.

Doesn't mean that it's right.
Assumption being one of the 'Mothers of All ???? Ups'

Leave this to Tony!
 
6.4A is wrong for a 2.2KW 400V motor. It’s for a delta connected 230V motor, for 400V you will have to connect it in star.


Tony I'm no expert on motors.

But you are right the 6.4A rating for a 2.2KW 3P motor is for a delta connected 230V supply.

For Star connected, 400v 3P 2.2KW motor the current will be 3.19A.

So a 6A c-type breaker will suffice with 1.5mm cable.
 
Duncan note on your second pic.... SY cable has been utilised to supply motor... but i see the screen has been taped off, make sure you earth the screen as its a possibility if the cable is damage it may become live otherwise, and Note! on my mcb choice, alot of people question why i have picked mcb's alot higher than expected, i cross reference them to manu' guides of mcb's and recommended mcb in relation to motor size.... having said that a 2.2Kw would normally need a 16amp(b) or a 10amp(c); In your case the motor current FLC (full load current) is that of a 3Kw motor hence i have thus given the mcb rating for a 3Kw motor. Following this advice you will eliminate periodic nuisance trips due to inrush.
 

Reply to 3 phase motor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked if I can wire a motor for a car lifter in a domestic garage, however the motor is 3 phase and only single phase is available in...
Replies
5
Views
821
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi, I am looking for a connection diagram or sugestions for a 2.2Kw single phase motor to drive a compressor. The spec plate shows that it can be...
Replies
5
Views
755
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
335
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
590

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock