hi chaps, I've got a 3-phase supply to get in and am not overly experienced in 3-phase cable calcs, basically the run is 60m, it will be buried, and it needs to run one 3 phase 16A boiler, a couple of single phase socket outlets and a couple of lights.

hope somebody can shed some light
 
just calculate the current per phase, then select the cable size accordingly, not forgetting volt drop.
 
earthing arrangements and adequacy I know, I have done this and its all good, the submain is coming from a Merlin dis board right at the incomer, sorry i should have said,

i have calculated that 6mm 4 core should be plenty for the job, and thats okay on the volt drop side of things even on a much longer run, seem good to everybody?
 
Without working it out myself 6mm sounds a little undersized can you show your calcs pls... im surprised at that length on a 32amp supply meets VD... and as others have pointed out you need to decide if you are just extending your earthing system or whether your set-up requires additional earthing from the supply or alternatively the use of earth isolation and TT -set up been done.

Do you have structural conductive parts, do you have other services in the boiler house brought in conductive pipework?

I feel you have just plucked 6mm out of thin air here and waited for someone to comment - we need all the info for us to comment and we need to see your calcs if you want guidance to the correct cable.
 
Why is it when you ask for an OP to show calcs as their posted alledged calculated answers dont seem right we end up talking to ourselves ... we are trying to help but if they refuse to help themselves by posting their calcs then we wont bother helping them seek the answers they are after.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3-phase sub-main sizing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
suffolkspark,
Last reply from
Richard Burns,
Replies
21
Views
6,841

Advert

Back
Top