Haha i like it. So it okay to do or not
Yes.Thanks spindon. So if you have two showers then you got 64amp flowing down the neutral but if you put the third on then it cancels it out?
Hence why I suggested 16mm2.Okay thanks so the cable needs to be able to handle 64 amp then.
They will. You will draw less than 32A but still nowhere near 0A.Got ya. Why wouldn't just two phases cancel each other out a bit?
.Picking up the big hint from @westward10 - I had a go at a phasor diagram. If phase 1 shower is on, I get 30A (say) on the distribution circuit N. If phase 1,2 and 3 showers are all on then I get 0A on N, as they all cancel out. No big surprise as it's a balanced 3 phase load at that point. So what about when 2 showers are on? Hint - I was wrong before in #14 - it's my brain that's been flogged.
Okay just been speaking to some that said even in the worst case scenario on an unbalanced system the neutral current will not exceed the highest of the phase. So if it's a 30 amp circuit then the maxmima neutral current is 30amp.
So many different responses and its clear I'm not the only one confused on this.
Cheers
A shower passes a current of Iphase.
There are 3 phase currents I1, I2 and I3
Taking I1 as reference at 0deg, the I2 is =120 phase angle and I3 is 240deg (or -120deg)
Assume two showers on using I2 and I3, then In is I2 + I3 =
Iphase(cos120 +jsin120) + Iphase (cos-120 +jsin-120) =
Iphase (-0.5 + j0.58) + Iphase(-0.5 -j0.58)=
Ip (-0.5 + j0.58 -0.5 -j0.58) = -Iphase = -7000/240.
If you now add in a switched on I1 fed shower In = I1 + I2 + I3 =
Iphase-Iphase = 0