@Leesparkykent So looking through the regs you quote, clearly cant dispute anything there. But still back to my original question why are you using the main fuse for your calculation? My thinking is that a fault occuring will be from the installation itself rather than the DNO equipment. And anyway I am surely only looking at the installation after the DNO equipment. It is important to get this clear in my mind for obvious reasons. So again looking for the reasoning behind using DNO equipment for calculations (thats their business aint it) Sorry to be a pest, and perhaps ignorant but .....I am
 
My thought was to use the service fuse for calcs as it's the worst case. A tail shorted to earth in the metal CU will see all electrons fleeing through that wee cable, I think.
 
@Wilko Yeh I can see that and test is required at origin of installation, and of course we want the biggest "bang" possible in calcs. But you can see I based my calcs (mistakenly?) downstream and Leesparkykent upstream the difference being me thinking 4mm² is ok and Lee proving its not. Quite a serious difference which worries me. I know I'm being like a dog with a bone but I beleive its important to understand this from a regs and science viewpoint. And also what I was taught and what seems to be reality have a dangerous divergence potentially. Unless I misunderstood what I was taught on C&G course (entirely possible) anyway I will shut up now and mention it no more....
 
It would depend where the fault was in a circuit/circuits. Closer to the origin the higher levels of fault current hence sizing the main earthing conductor to the worst possible scenario based on Ze. The fault current/level diminishes with impedance.
 
Might be using this job for my niceic annual assessment later this month
although i am likely going to upgrade the 6mm (I doubled checked and it does look like 6 rather than the 4mm i orignally said) to a 16mm from supply cable to MET- just to give the niceic guy no room for argument!

although would be nice to understand for my own mind and the future etc....

S= SQROOT I² t/k

SQROOT 1277.77² x 0.2 /1.43 (used the 0.2 as per fig 3.1???)

= 3.96mm²

so theoretically the 6mm² would be fine- but do I stand by this or by table 54.7 saying it needs to be minimum of 16mm²
 
i would say min of 6.0mm for TN-S. the reason 6.0mm is adequate is that it's the length of time the fault current flows that determines whether or not the earthing conductor can withstand it. basically, the energy dissipated is dependant on current and time.
 
A
544.1.1 comes in to play here where it states the earthing conductor for the installation shall not have CSA of less than 6mm. 132.6 The CSA of conductors shall be determined for both normal operating condition and, where appropriate, for fault conditions.
As far as I am aware, that applies to bonding conductors, not earthing conductors.
My understanding is that the minimum CSA for an earthing conductor is 2.5mm2 if provided with mechanical damage, 4mm2 if not (543.1.1).
 
Hi Spin - yes reading just now it starts with 543.1.1 which immediately sends me off to 543.1.3 and 543.1.4 , and then goes on to say it shall not be less than 2.5 or 4mm. Which I only saw after not following their direction to adiabatic eqn / selection table sections. Ha ha. That hit my funny bone and reminded me of the famous bomb disposal manual :
step 12 cut the blue wire (turn page)
step 13 but before cutting the blue wire ...
 
It needs upgrading. Is it def a bs951 clamp? some older installations it looks like a bs951 clamp but its actually shaped/grooved to accommodate the cable. If it is then you could just replace the 4mm and put a safety electrical connection do not remove tag on the cable. If not you could make a call to the DNO and they will prob come out for free and put a Hepworth clamp on it.

Lee dont suppose you know what the bs number is for these older curved clamps are do ya?
 