It's a small workshop with a 3 horse power table saw saw
The plan is to run 2.5 singles in conduit to the 20a switch for the saw; a 16a C type breaker should accommodate the start up induction current (around 15a and then run @ around 9a).
Lighting in conduit to wall plate level then in minitrunking to HF fluorescents, with non maintained emergency bulkhead on the phase.
RFC on 32a RCBO
Have I covered it?
That all looks fine Lionel.