Wrong.
Designed several, including some for the UK.
I'm happy to be corrected.Tell me where. Where can you buy 133v appliances.
Parts of Europe used to have 220/127 but I have never come across 230/133.
It's not a 133v appliance.
It was a 230 single phase appliance. With a converter to change to 3 phase 230v.
Individual elements were rated for 130v because of the star configuration.
I have a British-made 3-phase generating set rated to produce this voltage for powering radar installations, which took a 230V delta supply although the generator is star wound. I have seen mention in a data book of 135V historically in China and possibly 133V in Northern Italy, when lighting and power services were supplied at different voltages and tariffs. Some voltage selectors on European valve universal radios encompass 133V, with tappings as high as 140 or 150V, although mainly to allow them to be set to the actual voltage rather than the nominal.
I think the point of this thread was that the OP was surprised that the elements seemed to be passing too much current and this was one possible explanation that could be eliminated by checking either the rated voltage of the elements or their original wiring configuration, neither of which has happened yet.
Also how has the N connection been produced, can you post up a diagram of the wiring arrangements?
Hi Pete,My friend sent me this. I still didn’t manage to re run this thing. Please recommend wire sizes and if 3ph to single phase conversion was made, what will be my effective current requirements? Will a 25kva transformer be enough?
Again its a 230V 9kW 3ph immersions heater originally. My friend from india said that it requires around 63A if current when it was at its 3phase form.
Can't offer "how to" advice From a distance Jon, not knowing your Skill set, best call a local electrician in your location.
If you are running all 3 elements on the same phase, be aware the neutral current will be the sum of all the loads.
Jon with all due respects to your Friend in India, The diagram you linked is just a diagram of how a 3 phase Star connected load is connected, and how the N amd E are derived from this system, your post leads me to believe you don't trust your Friends' judgment of the situation, asking for a second opinion on an internet Forum is not good advice in this situation, like I said earlier you need to contact someone local to you, for help and guidance. That is the best advice I can give you.