here's a bit of as tickler for you (or for me anyway)...

when doing a resitance measurement on a three phase supply, how come i am getting a reading of zero ohms across all three phasses ie. dead shorts? (L1 - L2, L2 - L3, L3 - L1 ALL EQUAL 0 OHMS)

i understand that when measuring the voltage i have a reading of 230v between each phase and earth, and when measuring between any two phases am getting 415, all fine, understood.

but what i dont understand is how there can be a potential difference in voltage for my 415v when a resistance reading is giving me dead shorts, surely this would indicate no voltage difference?

why is there a dead short reading between phases?
 
it is not a periodic test, was renovating a machine and came across a faulty 3-phase socket, spent about 2 hours trying to find a fault in the machine, turns out it was the dodgy socket. so one thing lead to another, including this thread
 
Thats a strange one! When was the instrument last calibrated? Have you tried testing the resistances of known items, such as a 100ohm resistor or the like. See what readings you get?
 
I'm pretty thick :confused: and can't visualise where you're testing resistance...

at the socket with the supply off (so back towards the DB)?

at the machine plug (to the machine)?

Please can you elaborate?
 
ditto silva foxx i'm confused too, what test are you actually doing on what and how.
If you are testing live then it's impedance and would never be zero unless your meter is duff
If it's dead test and with continuity then you may be reading the winding of the motor or generator.
we really need some more info........... ;-)
 
Phase to Phase ie R1 of L1 + R1 of L2 resistance of the supplying cable, will most definately contain a resistance reading.
Please tell me you are NOT live testing between phases (400v) thats a big no no you will blow the internal fuse at best or fry your tester,could even put yourself in harms way. Has others have said could you elaborate what and how you have concluded a zero resistance reading between phases.:confused:
 

Reply to a little confused - 3 phase theory in the Canada area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
484
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
307
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
616
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
802
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock