Was sent to wire up a 3 phase saw in a small fab shop today god you could of condemned everything I saw but that wasn't why I was sent so new saw been put in place with isolator local so I glanced terminated and tested all ok but back at the board the breaker was. A c type 50a when I clamped the cables they were only pulling 16a per phase when saw was running I have advised the guy who owns it to down grade the breaker to c type 20a but he doesn't want to fork out the £40 for a new one were do we stand
 
The cable from the db to the isolator is a 4 core 10mm the saw has a pre wired cable to which I've connected it to the isolator but these cables only look 2.5mm
 
if its not correct for the job then surely you can just tell the customer it needs changing ?

if you say "it could do with changing" of course their going to go for the cheaper option of leaving it ??
 
Well yes it was running not cutting anything and it was pulling 16a per phase the saw has been getting used for years in another building so the 5 core 2.5mm cable that came with saw has been ok in previous building would you be happy to leave it on c type 50 a breaker or am I worrying to much lol
 
They've got 3 phase welding sockets hanging of walls cables exposed the lot ment to be going back again to remix sockets and generally make things safer a dirty job but its work
 
the breaker is there to protect the cable, the overloads the motor, 10mm2 may well be okay depending on the length, I haven't got the BGB to confirm.
 