nicsin02
Hi guys, I got called out to a jon today and the customer is wanting 19 lights fitted on his wall, these lighrs slot into the space of a brick thats been taken out, each light has a 20w lamp, 19 x 20 380W so roughly bout 1.5amps, there is already an outside socket fed from the ring, wouldit be ok if I spurred from outside socket into a wetherproof spur which then would go to a junction box under decking and I would run a flex to a photocell and then run an armour round all the lights, would this be ok? Would I need a contactor for 19 lights?
Another quick quesion, the same customer has fancy dimmer switches and the connections are "live" load" and " slave link" one end of a 2 way lighting circuit are these dimmers and the other is just a normal switch, connecting it as I normally would works fine when dimmer is on but when dimmer is off I cant switch lights on at the normal switch, any ideas, thanks
Another quick quesion, the same customer has fancy dimmer switches and the connections are "live" load" and " slave link" one end of a 2 way lighting circuit are these dimmers and the other is just a normal switch, connecting it as I normally would works fine when dimmer is on but when dimmer is off I cant switch lights on at the normal switch, any ideas, thanks