I have been asked to do some work in an old council flat and need a bit of advice.
There are 2 lighting circuits, 2 ring finals and a radial circuit in the property, all are run in pipe in the fabric of the building,
like you usually see in old council blocks. There is no earth run to the individual points but I can see 2 4mm earth cables
at the board. I have done a continuity test between the individual 4mm earth cables to the back boxes and pipes at a number
of switches and sockets and I am getting a good reading. I'll assume for now that I will get good readings at every point.
I cannot see where the 4mm earth cables run to from the board, I would image they are joined to the pipework just above the
board that has been covered over. Is this earthing arrangement adequate for protecting this number of circuits?
The client is thinking of replacing the old metal clad board with a split load RCD board. Will the earthing arrangement support this?
Will it even RCD protection as it is run in earthed steel conduit (BGB - 522.6.101?)
The socket outlets only have a single length of 1.5mm cable from the earth terminal in the back box to the terminal on the socket.
Will it be acceptable to just double them up?
The only changes being made to the old circuits will be changing the single s/o to doubles. Light fittings and switches are all class 2.
Sorry for the awful structuring of this post, I hope you can make out what I'm trying to get at!
There are 2 lighting circuits, 2 ring finals and a radial circuit in the property, all are run in pipe in the fabric of the building,
like you usually see in old council blocks. There is no earth run to the individual points but I can see 2 4mm earth cables
at the board. I have done a continuity test between the individual 4mm earth cables to the back boxes and pipes at a number
of switches and sockets and I am getting a good reading. I'll assume for now that I will get good readings at every point.
I cannot see where the 4mm earth cables run to from the board, I would image they are joined to the pipework just above the
board that has been covered over. Is this earthing arrangement adequate for protecting this number of circuits?
The client is thinking of replacing the old metal clad board with a split load RCD board. Will the earthing arrangement support this?
Will it even RCD protection as it is run in earthed steel conduit (BGB - 522.6.101?)
The socket outlets only have a single length of 1.5mm cable from the earth terminal in the back box to the terminal on the socket.
Will it be acceptable to just double them up?
The only changes being made to the old circuits will be changing the single s/o to doubles. Light fittings and switches are all class 2.
Sorry for the awful structuring of this post, I hope you can make out what I'm trying to get at!