Adam Smith

I have been asked to do some work in an old council flat and need a bit of advice.


There are 2 lighting circuits, 2 ring finals and a radial circuit in the property, all are run in pipe in the fabric of the building,
like you usually see in old council blocks. There is no earth run to the individual points but I can see 2 4mm earth cables
at the board. I have done a continuity test between the individual 4mm earth cables to the back boxes and pipes at a number
of switches and sockets and I am getting a good reading. I'll assume for now that I will get good readings at every point.
I cannot see where the 4mm earth cables run to from the board, I would image they are joined to the pipework just above the
board that has been covered over. Is this earthing arrangement adequate for protecting this number of circuits?


The client is thinking of replacing the old metal clad board with a split load RCD board. Will the earthing arrangement support this?
Will it even RCD protection as it is run in earthed steel conduit (BGB - 522.6.101?)


The socket outlets only have a single length of 1.5mm cable from the earth terminal in the back box to the terminal on the socket.
Will it be acceptable to just double them up?

The only changes being made to the old circuits will be changing the single s/o to doubles. Light fittings and switches are all class 2.


Sorry for the awful structuring of this post, I hope you can make out what I'm trying to get at! :P
 
As Glennspark says, and it is acceptable providing your test results are in spec, and i would give it a good going over before you quote and / or end up with a bag of worms.

If you are not familiar with this type of install, then whip off a few sockets and switches, you should find that the "pipes":wink_smile: (aka conduit) are fixed to the back box with a big nut (brass bush), at the cable entry. Your 1.5mm earth tags should be fine as long as they are mechanically and electrically sound. Visual and a tug for mechanical, and R1+R2 and Zs for electrical.

If it turns out that the install is shot, then rewiring shouldnt be too bad, just pull in the new with the old, and hope that none of the conduits are crushed with the fixings in the wall.

Enjoy,

Cheers...............Howard
 
Last edited by a moderator:
Cheers Howard.

I'll give it a good inspection and test it all before I price it. Luckily I am working for a builder I know so he will be flexible on the price. Do you think a board change is necessary? It is in good shape and if no RCD is required it might be a pointless exercise.

I am a bit loathed to replace all the cabling as it not run using conduit cable and from my past experience pulling cables in these flats as an apprentice, the 'pipe' on the top floor flats (as this one is) was knackered and all the cables were stuck fast. I don't think the client will be keen on running trunking all over the place!

I am up on the terminology but have spent too long working with other sparks who have their own names for everything. Usually leads to a lot of blank stares at the wholesalers (i.e Christmas trees = knock in cable tie plugs!)

Harryb - Bonding will be going in. There is a nice new partition wall going up that will get me most of the way from the board to the gas and water cupboard
 
make sure any knockout boxes using the containment as the CPC have either a fixed lug or a fly earth...
if your replacing the metalclad board then the earthed integrity of the containment will have to be maintained either by use of banjo (if using a PVC board)...or you could replace with a new metalclad unit....
 