No, it's only feeding that, it was always on a 16A so remained on a 16A/2.5,
I was just thinking of rigging up a relay with buzzer on the N/C contacts so it came on when the rcd tripped, but put of by the idea of getting woken up late at night!
Use the relay trigger to reset the RCD :-)
Have you tried linking out the room stat for a day ?
Just to eliminate that. I know you said it's RF but the sender unit is wired into boiler.
( depends on make whether this can cause it but there is nothing I can think of at the mo, if you've no MV's)
What type RCD? Type B maybe a Type C would help. Has pump motor got capacitor over it? Could be that.
Maybe worth a PAT test of the earth leakage of the feed into the boiler.
No, not tried linking stat out, it is a plug in unit so not sure how easy it will be, and not so easy as heating would be on all day?
16A type B rcbo, not looked inside yet, but will keep you updated, think first port of call is swap Rcbo and check pump.
Pump works on heating and hot water so it's been working all the time.
have you got a frost stat anywhere ?
No, no frost stat, had a look inside, no signs of water anywhere, have swapped RCBO with the 16A rcbo for external socket, will see if situation improves.
Update,
Swapped boiled over to external socket rcbo and heating has never went off since (fingers crossed) however I notice the old rcbo has tripped even though it has never been used(now on the outside socket), new rcbo coming courtesy of the supplier FoC
No, but it is less than a meter long and is brand new cable as I put it in myself.
Have you tested the RCBO ?
You could clamp the Line /Neutral to see what the boiler is leaking that might give a clue.
Swap the RCBO for another just incase its a internal intermitant fault with the internals!
I would if I had test gear.
I did swap the RCBO and it's cured the fault on the boiler, but tripped randomly when put on the external socket,
The RCBO is at fault.
So you are doing installation work, and investigations without test kit!
You can't say the RCBO is at fault if you haven't tested the circuit, OR the RCBO properly...... think about it.