Discuss Amount of sockets on a ring in the Australia area at ElectriciansForums.net
M
markharris
Osg says that a socket circuit's diversity is calculated as 100% of maximum point of utilization,then 40% of remaining points. To me that means the max sockets you can have for a 32a ring would be only be 4 sockets!!!!!
Obviously I am interpreting this info the wrong way, but can anybody explain the rules governing how many sockets you can put on a 32a ring for example?
Ok, but would having six four way extension leads plugged into 3 double sockets so 12
Appliances (computers/printers/Internet hubs) cause a 32a mcb to trip on a 32a ring?
No mate, all IT equipment works on earth leakage, most pc's work on around 3.5mA earth leakage, so put more than about 8 items on any RCD rated at 30mA it will trip, dont forget its not just one circuit on a RCD but many, so even if your little array of extension leads dont eport 30mA add it to other circuits and it may well!
Thanks high tower, so I guess you still have to assess the amount of equipment with the amount of sockets that you will have when designing your circuits, even though it will fall within the 100m floor surface area,and not just have an unlimited amount.
If your designing circuits that carry large amounts of IT equipment you then get into the position of splitting circuits into smaller circuits, with RCBO's and high integrity earthing.
Do the maths. Add up the loads, and divide it by 230, if it is less than the rated capacity of the protective device then you are fine. As stated excessive use of extension leads is not good, but at least make sure they have a 13a fuse fitted so as not to overload the point in the ring where it is connected. And i also agree with the comments regarding RCD tripping.
Cheers......Howard
Reply to Amount of sockets on a ring in the Australia area at ElectriciansForums.net
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
  • Locked
5K