Hi Guys
I hate being beaten but this has got me scratching my head.
Got a lighting circuit thats tripping the mcb (6A 1.5mm t&e), RCD doesnt trip so has to be overload ("has to be" is taken with pinch of salt please!)
All bulbs out - trips
SELV disconencted - trips
all switches unwired - trips
IR test r1+rn >200 ohms r1+r2 >2ohms r2+rn >200 ohms
continuity test - fine
getting a bit annoyed at this one...anyone any bright ideas ?...(get it..Bright..lighting circuit)
It has to be a wiring fault but im at a loss now
find the approx. mid point. dis the ougoing leg. see if it trips. then depending on whether or not, go back towards CU if still tripping, or away from CU if the first bit of the leg is OK. and i don't understand what you have posted re IR tests. they should be L-N, L-E, N-E.and result should be in Mohms , not ohms.
could be a faulty breaker, then. try replacing it before more head scratching, or temporarily shift the circuit to the other lighting circuit.(don't forget to move the neutral if they're on different RCDs though)
thanks telectrix
when you have eliminated the impossible, whatever remains, however improbable, must be the truth ...in desperation rigged up a single 40W light on a totally NEW short radial with one switch, wired to existing MCB – IT TRIPPED !! new MCB and all is fine..
MCB is faulty !!....now I’m annoyed at myself for not trying that 1[SUP]st[/SUP]
Oh well lesson learned
thanks guys...most of a day spent on site for an MCB !!
oh well sometimes you win sometime you loose !!
Own fault should have considered it earlier
Reply to any ideas..lighting circuit keeps tripping in the UK Electrical Forum area at ElectriciansForums.net
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...